    Converting 200A mobile home service to standard residential
    I currently have a 200A meter/main shut-off enclosure on a pole that was intended to support a mobile home. It is grounded with a #4 wire and rod right below the enclosure. With the mobile home now gone and a garage built, I'd like run power from that main shut off underground 125' to feed the service panel in my new garage. I'm planning on using 4/0 4/0 2/0 AL direct burial with no-ox on the connections. My question relates to the ground. Do I run another #4 bare wire the length of the run from the original grounding rod directly to the ground buss in my new panel? Do I need to install another grounding rod right outside my service panel? And am I correct in thinking that if my neutral and ground are bonded in my main shut off, then I'd NOT bond them again in my distrobution panel? I have a well and plastic piping entering my garage. Thanks in advance.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 9, 2011, 07:30 AM
    The service neutral is grounded at the pole service and establishes grounding at that point.

    From the pole to home a 4 wire is needed. You mention 3 wire URD cable, and you should use 4 wire URD cable, that will have the equipment ground from the meter/disconnect to the panel in the home.

    The neutreal in the panel will need to be separated and isolated, and the equipment ground conducotr will need to connect to an equipment ground bar in the panel.

    No, do not drive a ground rod at the home.

    If you have any metal piping in the home it will need to be bonded to the equipment ground bar in the panel using a min of #8 copper.
    mainestate's Avatar
    mainestate Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 14, 2011, 05:57 PM
    Perfect! Thanks for the concise easy to follow answer.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jun 15, 2011, 02:41 AM
    I just noticed your name, from Maine also. At the service pole there should be at least two ground rods at least 6 feet apart, per state code. Helps with the quality of grounding.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

A/c no different for mobile home then standard home [ 1 Answers ]

I have a coleman evcon dgat070bde furnace and we want to add central air. (2 summers ago husband bought unit off craig's list used and the person selling it came out and installed an a-coil and a drain something or other, I think the unit it only a 1 ton anyway it cooled somewhat the 1st summer but...

Mobile home service [ 4 Answers ]

I have a 200a service for mobile home will be adding another mobile can I add another 200A load center @ power pole come out of existing panel to feed new box?

Mobile home supply valves - non-standard sizes? No adapters? [ 3 Answers ]

I recently bought two appliances that need a cold water supply - a drinking water filter that mounts under/on the kitchen sink, and a self-cleaning cat box. Both come with T-valves that screw onto the supply valves, providing water for the appliances and the sink or toilet. The water filter...

Mobile Home Service Wire [ 5 Answers ]

I just bought a used Mobile Home - The previous owner moved the meter box from the back to the front - It has not been hooked up to the electric company since then - I know he should have done it with a permit - but I am now the owner. I am not an electrician. I live in Manitoba Canada. Here is the...

Mobile Home Electrical Service [ 6 Answers ]

Thgis is a combination electrical/legal guestion. Who is responsible for the service drop in a mobile home park? I live in Pennsylvania and was recently told by a human services agency here that weatherization could not be started on my mobile home until a problem with the main electrical...


View more questions Search