    Grounding an added circuit in a main lug panel
    I am installing a 30 amp single pole breaker into a Square D main lug panel and need to clarify where to attach the ground wire. Do I attach it to one of the neutral bars, or do I need to install a separate ground bus bar to attach it to?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 9, 2011, 04:41 AM
    A MLO panel may not have the Main Breaker contained within it, therefore, the neutral bar is for neutral conductors only, and the panel should already have a separate equipment ground bar.

    Only in a panel that has the Main Breaker allows the neutral bar to be for neutrals and equipment grounds to connect.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New 250 volt circuit, no grounding bar in main panel [ 4 Answers ]

Hi, I have searched for this answer but I can't find a clear answer for a rookie. I am adding a 250v/20amp circuit to my main panel for a window air conditioner. I have a newer Murray main panel that was installed by an electrician, but its an old house and all the outlets are 2 prong type. So I...

When can you use a main lug only electrical panel [ 1 Answers ]

I am install a 400 amp 480 volt panel outside a building. It will be fed from a breaker inside. Can this panel be a MLO or does it have to have a main breaker or disconnect.

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Main lug panel [ 1 Answers ]

I have a 150 amp main lug panel supplying all the electricity for my house. I have not found any main disconnect for this load center so I'm assuming the power company has to pull the disconnect at the meter. There is a 60 amp double pole breaker on the top section of the hot bus that appears to be...

Main lug panel installation [ 2 Answers ]

I have spliced into a 220 feed running to my pump house to run power to a playhouse. There were 3 direct burrial #6 awg cables. When I tracked them I had 2 hot and one Neutral, No ground was ran with them. At the pump house the panels ground bar was grounded by copper and rebar into the earth....


View more questions Search