    Nuetral to ground resistance 120volt 20 amp electric circuit?
    What is normal nuetral to ground resistance on a duplex receptacle, 120 volt 20 amp circuit in an office setting?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 4, 2011, 09:27 AM
    There is no "normal resistance", as it will change due to length of conductors, reliabilty of connections, etc.

    This is not a valid value, since the only connection between both are at the "single point of coupling" of a service.

    Why do you ask?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    May 4, 2011, 02:45 PM
    Assuming everything is wire nutted properly and grounded at the box and that no one has switched a hot for a neutral, it should read zero or close to it. Unless this is a relatively new install, neutral and ground are on the same bar in the box. Even if you have separate neutral and ground bars, it should still read zero. Copper wire has great conductivity and unless you are running a long distance it will not be increased that much. Standard wire gauge tables show 12AWG at <2 ohms per 1000 ft.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Allowable ground size on 80 amp circuit [ 0 Answers ]

Running 70 amp circuit breaker on #4 THHN stranded feeding a 3 phase 20hp motor. Motor FLA is 54, NFPA says 59, can I run a #6 ground?

Can a receptacle ground be attached to white nuetral terminal for ground? [ 1 Answers ]

I have older house. The receptacle showed "open ground." I connected a wire from the green ground terminal to the nuetral terminal, and the meter read "correct." I left it that way because everything worked. Is it safe?

Correct method to RUN copper ground wire to ground a 200 amp electrical circuit box? [ 0 Answers ]

Is a 3-wire copper ground or a solid copper wire required to ground a 200 amp electrical box? Is this wireing correct: A 3-wire copper ground wire in a conduit run from the electrical panel to the copper rod in the ground then to the cold water; AND THEN IN THE GARAGE the naked 3-wire...

The ground for a 30 amp circuit [ 2 Answers ]

I have a travel trailer 30 amp electrical cord. I am wiring a new male end on it. I have a white, green and black wire. Which is the ground? Thanks

Nuetral electric wires tied together in a 5 switch box [ 2 Answers ]

I have a wall box with 5 light switches, the neutral 5 wires are tied together, I want to replace one of the switches, it needs the neutral wire to function. How do I find the correct neutral wire that belongs to this switch. Or any neutral will do? Thanks in advance.


View more questions Search