    john1974's Avatar
    john1974 Posts: 5, Reputation: 1
    New Member
     
    #1

    May 1, 2011, 04:07 PM
    Derating cables
    I am installing two 12/3 uf cables in a continuous 1.5 pvc buried pipe from my basement to a backyard pull box for landscape lighting. How much must I derate the two 12/3 uf cables because they are in a pipe?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    May 1, 2011, 07:01 PM
    Other than for possible protection, why are you running in conduit? UF are direct bury cables. Are you running a 3 way switch too? Most landscape lighting is timered on a single pole switch with 12 or 14/2?
    john1974's Avatar
    john1974 Posts: 5, Reputation: 1
    New Member
     
    #3

    May 1, 2011, 07:42 PM
    I am installing two 12/3 UF cables in continuous pvc pipe for extra protection for the wires and I would like to know if I have to derate the wires?
    john1974's Avatar
    john1974 Posts: 5, Reputation: 1
    New Member
     
    #4

    May 1, 2011, 08:01 PM
    Comment on ma0641's post
    Yes I am installing the 12/3 UF cables in pipe for protection. No, I am not running a 3-way. The wires are for several SP switches and spares for future.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    May 2, 2011, 02:39 AM
    More than 3 current carrying conductors, up to six, will need to be derated 80%.
    john1974's Avatar
    john1974 Posts: 5, Reputation: 1
    New Member
     
    #6

    May 2, 2011, 06:45 PM
    Comment on tkrussell's post
    How many current carrying conductors in two 12/3 UF cables? Would you derate 80% of 25AMPS for UF cables?
    john1974's Avatar
    john1974 Posts: 5, Reputation: 1
    New Member
     
    #7

    May 2, 2011, 06:53 PM
    Derating
    When derating more than three current-carrying conductors in a raceway, does this apply the same if the conductors are installed in a cable? Example: romex installed through a contiuous pipe
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #8

    May 2, 2011, 07:02 PM

    You had about 7 posts on this yesterday, just kep adding your comments and questions at the bottom of your old post, on't start new ones each time
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #9

    May 3, 2011, 05:13 AM

    Explain how the 2- #12-3 cables will be used to determine how many are current carrying.

    The simple answer is all will be current carrying, and protect each circuit with a 15 amp breaker.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #10

    May 3, 2011, 03:00 PM

    Not sure I want to put my two cents worth in here but I'm going to do it anyway.

    You do realize that with two 12-3 cables you will have four individual circuits protected by 15 amp breakers. If you use three circuits now and keep one for a spare, that will give you 45 amps now and 15 amps for future use. If one were to assume 100 watt bulbs in each fixture those 45 amps would permit as many as 54 fixtures. Must be one heck of a landscape lighting project.

    You said you want multiple single pole switches but didn't say how many or what kind of fixtures.

    You said 12-3 cable, you do realize that 12-3 means 12 gauge wire with 3 conductors. Two hots and a neutral plus a ground wire. Meaning 12-3 has four wires.

    Something tells me that you are terribly confused. Why not tell us what you want to do and then let someone tell you how to do it.

    Tell us like this.
    "I would like to run power from my breaker panel to my patio. At my patio I would like to have four switches. I would like to have one switch turn on the front yard lights, the second would turn on the back yard lights and the third would turn on the side yard. The fourth switch would be a spare in case I decide to put lights on my roof."

    Just a suggestion.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Derating of Transformer [ 1 Answers ]

Hi every one Could anyone please advise me on how we can derate the transformer?:)

The cables of my ac are torn by my dog how can I change the cables? [ 2 Answers ]

The cables of my ac are torn by my dog how can I change does electrical cables?

Derating factor of cables [ 1 Answers ]

What is meant by derating factor.How it effects the ampacity of the cable.