    Applicable code is 2011 ICC.

    Trying to correctly set up a portable generator inlet box (4 wire twistlock) and run almost 20 ft through a finished garage to the transfer switch (which is mounted next to the main service panel). The intended genset is 7kw, 110/220v, and has integrated 30A breakers.

    Q1: Must I use SE for the run from inlet box to xfer switch, or is 10-3 NM acceptable?

    Q2: If I enclose a portion of this run in conduit for mechanical protection, do I size conduit like pulling THHN, or did I miss a derating factor?

    Q3: What is the proper grounding arrangement? (I got conflicting advice locally) The generator's frame is bonded to neutral. The manufacturer does not require (but does recommend) a ground rod be used.

    Q4: Is labeling for multiple power sources required on the main panel, and if so, may it be inside the access door with the manufacturer's label? The xfer switch powered circuits will pass through the enclosure, with wirenutted connections.

    Thank you!!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 1, 2011, 04:22 AM
    Good questions.

    Answers as follows:

    #1. NM cable is fine, assuming you have the typical transfer switch that does not switch the neutral. If the neutral is switched, then NM cable is not allowed, as the genset would be considered as a separately derived system.

    #2. Referring to Table 1 in Chapter 9, one cable shall be considered as 1 conductor in the conduit, and is allowed to fill the conduit up to 53%. You will need to find the cross sectional area of the cable, and find a conduit size that will only be filled 53%.

    Checking the specs of a popular brand of #10-3 NM cable, I find the diameter is .442 in, and will have a cross sectional area of .14 in sq. Checking Table 4 of Chapter 9 for Sch 40 PVC, I find that 1/2 In conduit can be filled with a cable up to .151 In Sq, so 1/2 in PVC is the minimum size conduit for a particular brand #10-3 NM cable.

    Keep in mind this is minimum, and need to consider the cable is solid wire, and consider friction of plastic against plastic.

    For a conduit sleeve for physical protection of a #10-3 NM cable, I would not use a conduit smaller than 3/4 or even 1 inch, depending on length of conduit and amount of bends in the conduit. #10-3 NM cable will not pull easy through conduit.

    #3. Grounding the genset with a rod is only required by NEC if the manufacture requires it. From the genset on, since it has a four wire receptacle, the neutral and equipment ground is separated and treated so through the transfer switch and each the neutral and equipment ground conductor simply connects at the panel's neutral and equipment ground bar.

    #4. I cannot find a specific code to address this at the moment, but considering that,assuming your using something similar to a GenTran transfer switch that only powers a few circuits, it is conceivable that both the generator and when the utility power is restored, the panel can have both power sources in the panel, and the panel should be labeled that there are two power sources available in the panel.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

House wiring and new gen set xfer panel [ 18 Answers ]

Thanks for reading this llloooooonnng post! Love to get the same answers more than once! I want to install a transfer sub-panel for emerg. Back-up from a 5550 gen. I am finding what I believe are issues with my house wiring, however. Outside I have a 200A main breaker in weather-tite panel...

3 wire generator to 4 wire xfer switch? [ 1 Answers ]

I have a generator with a 3 wire output(nema l6). It is 3000 watts and 120/250v output I have installed a transfer switch in the house that has a 4 wire input (nema l-14). Can I use this generator? Can someone explain to me the difference in the wiring between these two connector types. ...

Wiring a Wall Switch Questions [ 5 Answers ]

OK here goes... I got a automatic light switch (sensor) to replace a switch in my toddler's room. Currently there is a wall plate with two switches. (Prewired for a fan). One switch is for the fan and one is for a receptacle. In the wall (after I removed the wall plate) I noticed three...

Portable generator [ 2 Answers ]

QUOTE=tkrussell]The 100 volts is a bit low. Electrical device operate on +/- 10% , so the lowest volts supplied should be no lower than 108 volts. Incandescent lamps and electric heat will work fine on 100 volts. But any motors may overheat using 100 volts. Volts is usually changed on the...

Portable generator [ 2 Answers ]

The question I have is that my generator is only putting out about 100v. I would like to know if this will cause damage to anything that is running off the generator. Correct me if I am wrong but don't most appliances run between 110 and 120. I was told that the output of the generator could vary...


View more questions Search