    My Goodman CMP100-3 come on flames up but won't stay lit
    My 10 year old Goodman CMP100-3 come on, fan running, flames up for a few seconds, but won't stay lit. I have replaces the Flame sensor and have noticed that the red led on the HSI board stay lit. No flashing. Could my problem be the HSI board ($217)? Or something else?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Mar 18, 2011, 03:33 PM

    You say you replaced the flamed senser. How long ago? Probably not a board problem, but its not completely out of the question. I would check to make sure drain system on the unit is not plugged up at all. It may be worth having a pro in to assess the situation, as it may be a simple fix and cost you less to have it fixed by a pro than the price of a new board alone. I personally never replace a control board until all other components of the furnace are checked and then Im sure it is the board. Its never fun to replace an expensive control board, just to find you still have the problem.
    kwcarter's Avatar
    kwcarter Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 18, 2011, 04:16 PM
    I just repalced the flame sensor yesterday and the igniter 6 months ago. I have a Technical back ground. I even checked vacume line, all the Flame out sensors that are in series (0 ohms. There no obstruction in the xhaust pipe. I feel confident I can fix it I just wanted some feedback before I spent $ 217 (cost) on a HSI board.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Mar 18, 2011, 08:15 PM

    Okay. A plug in the drain system will cause one or both of the pressure switches to not operate properly. Does your unit have one, or two pressure switches. Either way, check to make sure neither switch is opening when the furnace fails.

    That being said, it really sounds like a flame sensing issue. Even with a new flame senser, there may be an issue with the wire, Or as you suspect, the board. You can test the flame senser with a multi meter. You need to set the meter to ua dc and put one lead on the flame senser connection, and the other on the wire that hooks to the flame senser (with wire disconnected from senser). The reading on the meter should be 2 or over 2 while flame is hitting the senser. If it drop below 1 - 1.5, the furnace will work intermitantly, or not at all. If below 2, there is a flame sensing issue, whether it be the flame senser itself, the wire, the board, or incorrect possitioning of the senser, or lack of flame (low gas pressure can cause this aslo). Its tough to really give great advice without putting my hands on the furnace, but Ill do my best to help out. Let me know how the pressure switches and flame senser test out, and we will go from there. Good luck, and please let me know what you find.

    PS. Also check to make sure the HIGH LIMIT is not opening when burners are burning.
    kwcarter's Avatar
    kwcarter Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 27, 2011, 12:35 PM
    Thank you for responding back. I did check those things and have a pro helping me. My problem is intermittant and I have been able to better asses my problem now that I have carefully watched the furnace. The bottom burner dose not always have a flame or has a problem in keeping flame up. The top three burners are find. However the Flame sensor is on the bottom burner. It will continue cycle and run its normal pattern until the bottom burner can substane adiquate flame so the flame sensor can tell the HSI unit Hey I'm lit. I did remove the pipe from the furnace and checked and cleand my nozels. I even unloosen the bottom nozel and checked it visuall and blew into the pipe to make sure no obstuction was in there. It appears more clearly now the my problem is in gas flow but see no adjustment on the regulator. Now I'm scatching my head whether to replace the regulator.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    Mar 28, 2011, 03:36 PM

    The pressure should be adjustable on the gas valve. Have your Pro friend get gas pressure readings on inlet and outlet of gas valve and adjust as necessary. It may also be as simple as a dirty cross-lighter bar on the burners.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace comes on but won't stay lit [ 6 Answers ]

Hi my goodman furnace tries to lite but something cuts the gas right back off. Is that the gas regulator? And can I just replace the module on the front of it or do I have to replace the whole regulator? Thanks Brian

Goodman gmp100-3 pilot won't stay lit [ 3 Answers ]

We have a Goodman model number gmp100-3 and the furnace kicks on and the pilot fires on and then goes out I was thinking it may be a spider web in the orphus but I'm not sure where to find it at? If any has any information that would be helpful pleae let me know.

I have a goodman furnace that seems to not stay lit. [ 2 Answers ]

I found the same issue or question that was previously asked about a year ago regarding a goodman furnace not staying lit after it power cylcled off 2-3 times. I would like to see the response or answer that Junior________ received. (sorry didn't catch the full name of the asker)

Goodman furnace won't stay lit [ 1 Answers ]

I have a goodman furnace that goes like this. Inducer fan comes on, 10 secs later glow lights up, 10 secs later get blue flames 10 secs later blue flames goes out. Repeats 3 times I have replaced the flame sensor still same problem But here is the thing. I am only getting 10 volts to the...


View more questions Search