Ask Experts Questions for FREE Help !
Ask
    powerless101's Avatar
    powerless101 Posts: 3, Reputation: 1
    New Member
     
    #1

    Mar 17, 2011, 12:38 PM
    All the power on a breaker went out due to a space heater.
    The breaker did not trip but I flipped them all anyway. It came back on later and then tripped again. I figured out it was due to the space heater when someone plugged it into an outlet on another breaker and the same thing happened. Now there is no power on either breakers circuit! Help!
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Mar 17, 2011, 12:42 PM

    Power needs to be checked coming out of breaker, maybe burnt open a bad connection, I would test to see if you lost the hot, neutral, or both.
    If Both, then likely a GFI or ARC Fault tripped, If the neutral, then a connection or on neutral buss.
    If the Hot, it could be the breaker, or connections.
    Check all boxes on that circuit.
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #3

    Mar 17, 2011, 12:43 PM

    I assume the MAIN breaker isn't tripped? And you have power elsewhere.

    When you reset them, you did turn them OFF first then flipped them back on. I have to say that because there are some people aren't aware that's how you do it. And you can't assume. I have neighbors I've had to show that to 5 times already.


    Also... what Stratmando said applies as well.
    powerless101's Avatar
    powerless101 Posts: 3, Reputation: 1
    New Member
     
    #4

    Mar 17, 2011, 12:50 PM
    It's not the main, the rest of the house works, but I flipped it off, and all the others, then back on. I'm still wondering why it would come back on the first time. Also, all of the outlets read hot/ground reverse on one (the one that came back on later) and correct on the other. Both have light switches and one has ceiling light. Neither have power to anything
    powerless101's Avatar
    powerless101 Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 17, 2011, 12:52 PM
    Comment on powerless101's post
    Now the side that is just outlets and wall switches to the outlet is working again, the other side is still off
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Mar 17, 2011, 01:00 PM

    Power needs to be checked coming out of breaker, maybe burnt open a bad connection, I would test to see if you lost the hot, neutral, or both.
    If Both, then likely a GFI or ARC Fault tripped, If the neutral, then a connection or on neutral buss.
    If the Hot, it could be the breaker, or connections.
    Check all boxes on that circuit.

    Also it would be a good idea to remove recepticle(s) and verify the white wire is on the silver screw, and the hot is on the dark screw.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Mar 17, 2011, 01:05 PM
    Many times a short circuit or an overload causes a weak or loose connection to open permanently. You may need to open receptacles, switches junction boxes looking for a loose connection.

    A popular location is at receptacles, esp if the wires are pushed into the back of the device, rather than wrapped around the screw type of connection.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Breaker shows power but no power to outlets [ 1 Answers ]

I have a breaker that is showing power coming out but all outets and equipment on this circuit are dead how do I find the problem?


View more questions Search