    I have a Lennox G40XH(X) series furnace and my ignitor never turns on (never burns).

    I really don't want to call someone in to fix this... any advice is greatly appreciated, but seems all other troubles I have read are further down the path in the furnace startup...

    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Mar 15, 2011, 03:37 PM

    There are many reasons for flame failure and you give no details at all. Are there code lights visible through the small peep hole? Archived Documents | Air Conditioners | Heat Pumps | Installation and Operation Instructions :: Lennox Residential
    mamforge's Avatar
    mamforge Posts: 4, Reputation: 1
    New Member
     
    #3

    Mar 15, 2011, 05:02 PM
    The LED lights tell me either my igniter is broken, the ignitor circuit is open, there is improper ground, or the voltage line is below 75V. The details are the thermostat is working and I have set it to a temp higher than the actual, the air combustion inductor initiates momentarily and then within a second fails. I checked all the leads and made sure they are properly connected. I am thinking it's the ignitor, but it died all of a sudden and not sure that is normal or if there is usually some warning.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Mar 16, 2011, 07:21 AM

    Most furnaces have reset buttons on the lock outs but if you do not know where they are or how to test for a failed part you may still have to call for a pro
    mamforge's Avatar
    mamforge Posts: 4, Reputation: 1
    New Member
     
    #5

    Mar 16, 2011, 06:19 PM
    I also measured the resistance on the ignitor and it was on order of mega ohms so def something wrong - it fried itself. To remove the ignitor on this model of lennox furnace I had to remove top tray above burner rack, the burner rack itself and then the ignitor. I picked up a new ignitor and the furnace fired up immediately.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox Furnace series g32Q [ 0 Answers ]

Air inducer starts, runs for a couple of seconds, then shuts down, nothing else happens. LED's indicate normal operation.?

Lennox furnace elite series [ 4 Answers ]

Problem with Lennox Elite Series... Burners will start but blower motor will not... can you cast any light on the subject... Thanks signed... Cold Chicagoan

Lennox elite series ac, exaust motor turns on then off [ 2 Answers ]

When I turn the Lennox Elite Series ac unit on it runs for about 25 to 30 minutes then the exaust motor shuts down, then I turn off unit, wait 15 minutes turn on runs fine for about 25 to 30 minutes and shuts down again. Is there a heat sensor that may be shutting it down, when getting to hot?

I have a lennox outside a/c unit and a lennox g26 series furnace.Low hum no air/ht [ 4 Answers ]

Lennox Value Series... serial 5896G56798 M/N 10ACB365-5 P Central a/c unit and a Lennox G26 Series gas furnace both about 13 or 14 yrs old. Came home from vacation and turned A/C on (son tried earlier in the week) only a low hum whether on auto or fan or if we try heat(same thing, low hum)......

Lennox G26 furnace fan turns on by itself! [ 1 Answers ]

Hi there I have a Lennox G26 furnace and a week ago, the furnace fan would just turn on by itself (the thermostat would be off at the time) and start blowing cool air. I would then try turning the thermostat to heat or AC, but it would continue to blow cool air. And it wouldn't turn off! The...


View more questions Search