Ask Experts Questions for FREE Help !
Ask
    jsr909203's Avatar
    jsr909203 Posts: 1, Reputation: 1
    New Member
     
    #1

    Feb 15, 2011, 03:14 PM
    Can I use 4 ga welding cable wire to power a 100 amp sub panel?
    I'm trying to power a 100 amp sub-panel and have a spool of "CAROLPRENE (R) WELDING CABLE - 600 VOLT - 4 GA " wire and was wondering if I can use this to reach my goal?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 15, 2011, 03:23 PM
    No, notice the marking on the cable states "Welding Cable".

    First off, a "subpanel" must be fed by a wire fully rated 100 amps, either a #3 copper or a #2 aluminum.

    Second, welding cable is considered as cord, and cannot be used as permanent wiring method.

    #2 SER aluminum cable is very popular for what you need. Some areas require conduit, best to check with local codes to see what is allowed.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Feb 15, 2011, 06:49 PM
    I believe welding cable is considered "flexible" and as such is not permitted "as a substitute for the fixed wiring of a structure" NEC 400-8. The AWG may be the same but UL approval would not be the same.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire UF wire to run to new 100 amp service panel? [ 10 Answers ]

My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is...

Wire size for a 100 amp lug sub panel [ 4 Answers ]

Hi I have a 200 amp main panel, but it is a small 24 slot panel. It is full and I need to add three more circuits. I want to run a 100 amp main lug subpanel. The plan is to move the clothes dryer breakers to the new sub and use the existing location in the main panel to install a 100amp breaker...

Wire size for a 100 amp sub panel 200 feet away [ 8 Answers ]

I have a 200 amp main panel in my house and I just built a garage and am planning on putting a 100 amp sub panel in the garage. The garage is about 200 feet from my house and it has a 2 inch pvc stubbed out underground. I am wondering what size aluminum I would need to feed it, and if I can use a...

Wire needed for a 100 amp sub panel? [ 3 Answers ]

I am installing a 125 Amp Sub panel in a detached shed approximately 100' from the house. The subpanel has a 100 amp main breaker in it and I have a 100 amp breaker that will go in the main house panel to feed it. I will be using #4 copper THHN for my 2 hot conductors and neutral conductor and a #6...

100 amp sub panel wire size [ 2 Answers ]

I now have the 100 amp breaker installed in my load panel. I will run wiring from the load panel to a 100 amp sub-panel in an unground 80 schedule PVC. I believe I need to use #2 wire for the hots and the neutral. If this is correct, then what size ground do I use? Number 6? The sub- panel...


View more questions Search