    My 100 amp main gets hot and trips?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 26, 2011, 03:52 AM
    Either the breaker is overloaded, or, more likely, there is a loose connection at the Line or Load connections of the breaker.

    A Main cannot be worked on safely without disconnecting power to the Line Side by removing the electric utility meter, which must be done by a qualified electrician or the power utility. Many utility company's do not allow electrician to remove the meter.

    The heat created by a loose connection probably damaged the breaker, and a replacement will be needed.

    Call in an electrician to troubleshoot and resolve the problem.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 26, 2011, 05:02 AM

    Don't be surprised if it is recommended that the whole panel be replaced. Usually, as TK stated, along with the breaker the buss is damaged by the heat and arcing if the problem is on the load side.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running two 100 amp main panels from a 200 amp service [ 27 Answers ]

Greetings! I live in a rural country area. The electric company will be installing a pole, meter, and 200amp service with disconnect at pole. (It will require 50 foot run of service cable from pole to main load center in mobile). Currently the double wide has a General Electric 100amp Main...

Can I run a 50 amp subpanel if a 100 amp main if so what size wire [ 1 Answers ]

Can I run a 50 amp subpanel from a 100 amp main and if so what size wire

200 amp main panel: 2 100 amp subpanels? [ 1 Answers ]

I was asked to by a homeowner to help with a wiring project. She has 1 200 amp main panel and 1 100 amp subpanel. Both are full yet she needs more circuits for a bed n' breakfast. Can another 100 amp subpanel be installed?

100 Amp Subpanel from 200 Amp main panel [ 2 Answers ]

I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...


View more questions Search