    Lennox G20 BCC does not keep fan running after heat demand satisfied
    Lennox G20 BCC does not keep fan running after heat demand satisfied. This is causing heat build up at the heat exchanger and causing the limit to trip. After the heat exchanger limit resets, the unit will come on again. I have replaced the BCC but the symptom remains. Any suggestions
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Jan 16, 2011, 07:33 PM
    If you have a air flow restriction-- Dirty return filter,dirty evaporator coil or just dirty cups on the blower wheel. All will keep the system from moving the air it needs to and cause a high limit trip.
    screaminbird55's Avatar
    screaminbird55 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 16, 2011, 10:16 PM
    I've cleaned it up pretty well. The fan does not run for the preset time after the gas valve closes (currently set for 270 seconds). If I manually run the fan for a minute or two, immediately after the valve closes, the high temp switch doesn't open and the next cycle comes on as expected.
    The switch only opens on the residual heat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox Whisper Heat G20 - Need control board [ 7 Answers ]

Model # g20-q314-100-1 Serial # 5890A05729 Need a control board for this furnace. The Q314 in the Model# may be Q3/4. The auto setting on the thermostat will not activate the blower fan. I had an HVAC guy come out and diagnose and this is what he told me. Is a Lennox part the only way to go?...

Lennox G20 gas furnace fails to start the fan [ 6 Answers ]

My Lennox G20 gas furnace ignites the pilot light and starts the main burners. The burners burn normally for about 2 minutes and shut down without the blower fan starting. If I manually set the blower fan to run continuously, the heater cycles on heats the house to the temperature set on the...

Tempstar heat pump AHU fan continues to run when t'stat satisfied... [ 10 Answers ]

I have a Tempstar split system multi stage heat pump with a Honeywell RTH7400D108 thermostat. My problem is intermittent and is that the AHU fan continues to run after the t'stat reaches the desired temperature. The outdoor unit will cycle back on when called for or I can open the breaker to the...

Lennox G20 with bad BCC [ 3 Answers ]

I have a Lennox G20 which I think has a bad BCC. It is having trouble starting up. It sounds like some of the relays on the board are bad. It is making an odd clicking noise on the board. It is Sometimes it does not ignite the burners and sometimes it does. When the burners do ignite, the fan...

20 yr old Lennox heat pump fan blows constantly in heat mode [ 5 Answers ]

20 year old Lennox heat pump - outside temps been 30's at night, 40's daytime UPDATE: I went outside and the unit is covered in frost on 3 sides! I've been reading on Google about frosted heat pump units and can't determine how to manually defrost it. Apparently, the auto defrost is not...


View more questions Search