    Do I just pull the main fuse to cut off power to the neutral bus bar?
    I have an old "service protector (pellet)" attached to the bottom of my service panel. I believe it is the old school equivalent of a surge protector (My and GE's tech support's best guess). The two wires to the hot side are already disconnected, probably because it was only rated for 175 volts, but the neutral side is still connected. I was just going to remove it, but I wanted to be sure pulling the fuse would allow me to safely do that.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jan 13, 2011, 07:37 PM

    Yes, when main fuse is removed or breaker is turned off everything in panel is de-energized except the incoming lines and terminals to the main.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Jan 13, 2011, 07:46 PM
    Is this a trick question? There is no "power" to the neutral... that's why it's a neutral. Now to be more clear power does go through the neutral via the two hot legs. The neutral completes the circuit. So if you have no power to either of the hot legs it stands to reason that there won't be any power to the neutral... right?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Jan 13, 2011, 07:58 PM

    You are correct of course Missouri. However, you could have voltage to the neutral buss through other circuits. For safety, the novice should always turn off the main before opening the panel. I think djm0730 just wants to be safe.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Jan 13, 2011, 08:03 PM
    HK... I wasn't suggesting that it be done with out the main pulled. It's always a matter of safety first and if you can shut it off, pull a fuse or lock it out it should be done. But pulling the main doesn't disconnect the neutral, and I believe that was the title of the question.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #6

    Jan 13, 2011, 08:14 PM

    See my edited post. Turning off the main insures no voltage to neutral buss.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #7

    Jan 13, 2011, 08:18 PM
    Comment on hkstroud's post
    ... as usual we are on the same page..
    djm0730's Avatar
    djm0730 Posts: 17, Reputation: 1
    New Member
     
    #8

    Jan 13, 2011, 08:59 PM
    Comment on Missouri Bound's post
    However I want power off to everything also going to the neutral bus bar. The same way you turn off two circuits if they are both present in the same receptacle box.
    djm0730's Avatar
    djm0730 Posts: 17, Reputation: 1
    New Member
     
    #9

    Jan 13, 2011, 09:00 PM
    Comment on hkstroud's post
    Thanks guys.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #10

    Jan 14, 2011, 07:21 AM

    There can be Electric Company problems that may have voltage on the Neutral even though the Main is shut down.
    To be safe, it doesn't hurt to stay Isolated(No contact with anything else).

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground/Neutral Bus in Main Service Panel - Is there a Difference? [ 8 Answers ]

I'm preparing to provide new wiring to a sizable addition to a log home. Prior to beginning the new work I mapped my existing circuits thinking it best to correct any potential overloads in the existing panel/circuit design before introducing any new problems on my own. Decided to make a few...

Neutral/Ground bus bar? [ 6 Answers ]

I am installing a sub panel in my basement to run some extra circuits for a bathroom, spare room etc. I am putting a 60 amp fuse in the main service panel, running a 6-3 wire with ground and back feeding the new sub panel. The new panel does not come with a ground bus bar, and suggests using...

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you

AC is turing off main power switch in the fuse box! [ 2 Answers ]

During Hurricane Ike, my house lost power and after the storm, when power came everything was all right except the ac. When I went to the fuse box(breaker), I saw the AC switch was OFF. When I flicked it to ON, it turned the main power switch to OFF and the whole house went dark again. I tried a...

Why is the grounding and neutral bus bar connected in the sub panel? [ 1 Answers ]

I had an electrician come in and install a new sub panel in my house and wire up my kitchen. When he finished, I took it from there. Now that I have the rest of the house wired, its time to connect it all to the sub panel. Both the neutral bus bar and the ground bus bar (2 separate buses) seem to...


View more questions Search