    How much current at 12 volts dc can 3 #16 ga wire handle 12 ft long all tied together?
    jcaron2's Avatar
    jcaron2 Posts: 986, Reputation: 204
    Senior Member
     
    #2

    Dec 20, 2010, 01:06 PM
    First of all, hopefully this is just a theoretical question. Even though I'm not an expert, I can assure you that in practice it's very dangerous (and against any reasonable electrical code) to rely on multiple separate (i.e. individually insulated) parallel wires to handle high currents. If one wire fails, the remaining wires will be forced to carry all of the current, but no circuit breakers, fuses, or other safety devices would be tripped. This is likely to cause a fire if the current is beyond their capacity. If possible, you should use a larger single wire instead.

    Secondly, the DC voltage (12-volts) and wire length (12 feet) are irrelevant with respect to ampacity.

    Finally, the answer to your question depends on the type of wire and the environment in which you run it, but you should be able to look up the current capacity of #16 wire of whatever type you have with a simple Google search. In theory, the DC capacity of three such wires run separately should simply be three times as much as a single wire. Or, if you can only find information for larger wire sizes (like #14, #12, etc.) then consider that three #16 wires have a total cross-sectional area (and, therefore, DC current capacity) that's somewhere between #11 and #12 wire. So you can just use the numbers for a single #12 wire to be conservative. For example, if this was plain ol' NM-B copper (a.k.a. Romex) or THHN copper, the maximum current capacity should be around 20 amps.


Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to calculate the short time current rating for current transformer? [ 4 Answers ]

Respected sir's, Please clear my doubts? How to calculate the "short time current rating"(i.e-primary short time current rating-like if u take 400-400/5-15va/class1,40ka/3sec). 40ka/3sec-how to calculate this rating from the substation? Is there any formula?please advise me... ...

The Petry Company has $1,312,500 in current assets and $525,000 in current liabilitie [ 7 Answers ]

The Petry Company has $1,312,500 in current assets and $525,000 in current liabilities. Its initial inventory level is $375,000, and it will raise funds as additional notes payable and use them to increase inventory. HOW MUCH CAN PETRY'S SHORT-TERM DEBT (NOTES PAYABLE) INCREASE WITHOUT PUSHING ITS...

Current transformer - short time withstand current [ 4 Answers ]

Hi, For ring-type (window-type) CT, do we need to size the CT short time withstand current at the same or above the system short time withstand current (short circuit level)? Any reference/technical explanation? Thanks!

Can Current Tenant Get Current Special Move-In Rates? [ 3 Answers ]

Hi Guys: My mother is living in apartments in Kissimme, Florida since September 2008 and the complex now has an offer for a 2/2 for $625.00 for a year's lease. My mother's payment is at least $100.00 above. Does she have any legal stand to try and get the lower price? She has asked me and I...


View more questions Search