Ask Experts Questions for FREE Help !
Ask
    Wilson2010's Avatar
    Wilson2010 Posts: 3, Reputation: 1
    New Member
     
    #1

    Dec 17, 2010, 10:25 AM
    Can I determine 60amp vs 100 amp service from outside home?
    Many insurance companies advise 60 amp service to home not acceptabble. Oftentimes homeowner upgrades with 100amp breaker box but service still 60 amp.My company states if service unknown then round meter on round base with 1 1/2" diameter conduit is 60amp service and therefore not acceptable. However, underwriter (UW) indicates if conduit larger than 1 1/2" likely 100amp so then eligible .

    Asked an electrician if 1 1/2" conduit with round on round always 60amp and he said "N0. If diameter of plug splicing wires together before descending to meter are approx thickness of little finger then 60 amp service. But, if plugs diameter of thumb than likely an older 100amp service." Home in question small frame ranch built 1954.

    Can you corroborate, or offer guidelines, to help make service determination without going to expense of hiring an electrician?
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #2

    Dec 17, 2010, 10:30 AM

    Wilson, do you not have access to the inside of the home?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Dec 17, 2010, 10:41 AM

    Let me confuse you more. A typical 100 amp service can use 3 #2 aluminum conductors, all in an 1-1/4" conduit.

    So the 1.5 in conduit theory is misleading.

    Then there is Service Entrance Cable, no conduit. Could be #2 but still have a 60 amp Main Breaker.


    There are so many variables, there is no safe "rule or thumb" to be certain of a service entracne size without looking at the rating of the Main Service Disconnecting Means.
    Wilson2010's Avatar
    Wilson2010 Posts: 3, Reputation: 1
    New Member
     
    #4

    Dec 17, 2010, 11:31 AM

    Appreciate your prompt reply!

    Given reply this is probable moot but for what it's worth wires on either side of splice appear similar in diameter.

    Yes, can access inside. If permit pulled and box indicates 100amp on the main then expect it's 100amp..

    But, if moonlighting electrician, or friend, updated fuses, or older breaker box with ato 100amp box without permit and didn't update actual service the main will read 100amp.

    If this being the case what do I look for?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Dec 17, 2010, 11:49 AM

    Which splice? The aerial cable from utility to the service entrance conductors in conduit on the building?

    Bad comparison, if so. Utility conductors are often reduced in size for various reason, or the wire size is small but the insulation is larger. In anycase, not a good visual to assume all is 100 Amp.

    If the panel has been changed to 100 amp and the remaining service entrance equipment and conductors have not been changed, or suspected, or not sure, one cannot assume this equipment is actually 100 amp rated without confirming the actual size of conductors and without reading the manufacturers label of the meter socket, which most times is not on the outside.

    Unfortunately, the only accurate method would be to have an electrician open the panel to confirm size of service entrance conductors, and open the meter to read the label. and confirm wire sizes there.

    Here is where is gets even more sticky. Many utility companies do not allow the electrician to pull a meter, for any reason, so they would need to be on site.

    I realize your looking for a quick fix to inspect a service, probably for an insurance inspection or risk assessment, done that been there, and there is none that I can comfortably pass onto you.
    Wilson2010's Avatar
    Wilson2010 Posts: 3, Reputation: 1
    New Member
     
    #6

    Dec 17, 2010, 11:51 AM

    Thank you!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

How do I know if my home has 100 amp service [ 1 Answers ]

How can I be sure my home has 100 amp service?

Can a 100 amp load center be used as a sub panel with a 60amp main breaker? [ 7 Answers ]

Hello, I`m triying to add a sub panel to my existing main panel. There is no more room in the main panel for circuit breakers and I wanter a sub panel with at least 10 more spaces.

100 amp or 200 amp service in new home? [ 17 Answers ]

We are having a home built and are anticipating having the following right now: 1250 square feet of living space C/A Fridge Separate freezer Washer/dryer Over/range Microwave Electric tankless hot water heater


View more questions Search