    National Electrical Code Online?
    What are the grounding requirements for water meters with metal underground watger pipeing coming into the building?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 16, 2010, 02:11 PM
    The NEC can be reached by using this Sticky Note found at the beginning of the Electrical Forum:

    https://www.askmehelpdesk.com/electr...ne-270277.html

    You will find:

    250.53 Grounding Electrode System Installation.

    (D) Metal Underground Water Pipe.

    (1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.

    Therefore, a bonding jumper shall be installed to jump out the water meter.

    Usually the grounding electrode conductor connected to the water line is left longer to jump out the meter.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Dec 16, 2010, 03:04 PM
    There are no grounding requirements for water meters. Are you talking about grounding the electrical service through water piping?
    mhpaavola's Avatar
    mhpaavola Posts: 2, Reputation: 1
    New Member
     
    #4

    Dec 17, 2010, 06:58 AM
    What gauge does the bonding jumper have to be for the water meter? What is the code number and requirement for grounding the service to the panel? Thank you.

    Marty
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Dec 17, 2010, 09:00 AM

    This "jumper" will be considered as a continuation of the grounding electrode conductor, therefore see Table 250.66, and related code sections.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #6

    Dec 17, 2010, 09:50 AM
    Table 250-66. Bonding jumper size depends on the size of the service entrance conductor but usually it is a #4
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Dec 17, 2010, 10:00 AM

    Ma0641, #4 copper is the grounding electrode conductor, or main bonding jumper, only for ungrounded conductors at #2/0 to #3/0 copper or #4/0 to #250 MCM aluminum.

    The term "usually" will only apply to services using the size service entrance conductors I mentioned, and the term "usually" should not be used so casually.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #8

    Dec 17, 2010, 10:46 AM
    Comment on tkrussell's post
    Well taken and struck from future vocabulary. Thanks, Brian

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

National electric code free online [ 16 Answers ]

What's the distance for gfci from water fixture?

Free online copy of the 2008 national electrical code (nfpa 70) [ 6 Answers ]

National fire protection association

National electric code free online [ 4 Answers ]

What size J box do I need? I have 2 -2 1/2 " emt conduits coming in with 4 250 mcm conductors?

National electric code free online [ 2 Answers ]

Are insulated recess housings required on the first floor of a two story residence if the first floor ceiling is not insulated?

National electric code free online [ 2 Answers ]

Outdoor uplighting requirements for low voltage and 120v?


View more questions Search