    Heather turn on but no heat with faul code 12
    My heather carrier 58PAV stopped working, The LE flash 1 short and 2 long , I checked the fault codes and with a short piece of wire,I short TEST/TWIN terminal to Com/24v terminal.
    Status LED will flash code then turn ON inducer motor, the motor ran, the ignitor heatup but no flames
    And the flashingcode is:
    12 BLOWER ON AFTER POWER UP (115V or 24V) - Blower runs for 90 seconds,if unit is powered up during a call for heat (R-W closed).
    What that mean and how I fix it.

    Thanks
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Dec 3, 2010, 05:07 PM
    When you run a test on the carrier system it will test all componen except the gas valve. What is the code after the blower shuts off after the 90 sec. with the heat calling?
    Kawa636's Avatar
    Kawa636 Posts: 4, Reputation: 1
    New Member
     
    #3

    Dec 3, 2010, 06:07 PM
    1 slow blink followed by 2 rapid blinks
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    Dec 3, 2010, 06:35 PM
    With the power off, remove the red thermostat wire from R on the control board in the furnace. Power the furnace back up with the Red thermostat wire diconected. What happens?
    Kawa636's Avatar
    Kawa636 Posts: 4, Reputation: 1
    New Member
     
    #5

    Dec 3, 2010, 07:23 PM
    Nothing at all
    When I press the door switch the LED light on but nothing happens
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #6

    Dec 3, 2010, 08:13 PM
    Tape the door switch closed. After you have the system powerd up use a jumper wire and jump from R to W on the furnace control board (with the red thermostat wire still disconected).Will the inducer motor come on? If so leave it jumperd to see if the igniter will glow and the burners light.
    Kawa636's Avatar
    Kawa636 Posts: 4, Reputation: 1
    New Member
     
    #7

    Dec 4, 2010, 08:11 AM
    Yes, the igniter will glow and the burners light up. I put everything back together and it work most of the night

    The problem now is that the heather can't keep up with the cold, it run but not for long... if I set the thermostat to 70 the higher temperature inside the house is between 60 to 65 never reach the settting temperature, it run but shut down within the next 10 -20 minutes,, and stay off for hours then kick back on blowing hot air... is driving me nut cause I do not know when I will have heather,, Did I mentioned that the Heather is 15 years old? Do you think is worthy spen more money in repair,
    I replaced the control board, 2yrs ago , the pressure switch, the igniter and for the AC the Hgh Voltage capacitor last year...
    Thanks for your time

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox heat turn off and turn back on to work [ 2 Answers ]

I have a lennox heater I have to turn it off and turn it back on to get it to heat. What is wrong and how do I fix it.

Heat blower does not turn - Air Handler does not turn on for heat [ 7 Answers ]

I have an Energy Kinetics System 2000 boiler. It is hooked up to two different zones (two different air handlers). Zone 1 (main house) when turned on at the thermostat clicks and calls for heat, the boiler starts for a bit but the fan/blower never kicks on. Zone 2 (master bedroom) works just...


View more questions Search