    What size cable for a 100a supply running at a distance of 100metres.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 7, 2010, 03:50 AM
    Need to know the supply voltage to do any voltage drop calculations.
    millhouse76's Avatar
    millhouse76 Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 27, 2010, 02:24 AM
    It's a 240 v supply thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 27, 2010, 05:38 AM
    Copper wire 7.348 mm will give less than 3% voltage drop,assuming the max load is 80 amps at 100 meters.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cable size 120 mm2 with matching lug size [ 5 Answers ]

Cable size 120 mm2 with matching lug size

Wiring from 200a box to 100a "" at distance of 40' [ 3 Answers ]

I am renovating the interior of my garage and I would like to put in place a 100a box. I am to be wiring from the existing 200a box which is located 40'+ from this garage. The 200a box is in a single unit with the meter. I would like to know if I should run it underground (if so, what wire type,...

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...

Supply line won't stop running. Main water supply off [ 3 Answers ]

I was doing some bathroom remodeling and attempted to remove an old supply valve. It would not budge so I decided to cut the copper tubing underneath it and put on a new shutoff valve with a compression fitting. The problem is that water just kept coming out of that supply line. The main water...

I need a 100A subpanel from parallel 100A main panels [ 3 Answers ]

I'm planning to install a low voltage driveway snow melt system that will require 70A (240V). I want to run this from a new 100A subpanel in my attached garage. My problem is that my 200A service is split into two 100A main panels. How would I accomplish this? My other option I suppose is to run a...


View more questions Search