    False Tripping GFCI and SPAS
    I have a 240volt spa, and I hooked the electricity myself. I installed a 70 AMP breaker at the main panel and purchased a spa panel from Lowe's. The panel includes a GFCI 50AMP breaker and includes extra places for lighting and what not.

    My spa requires 4 wires (2 hots, neutral, and ground). I believe that I hooked everything according to specs. My spa has worked fine with one aggravating problem. Once every few days (inconsistently) the GFCI breaker trips. I have researched this and have found that the problem is common especially in hot tubs with ozonators?!

    The only thing I have found is that I may need to purchase an expensive GFCI disconnect, which I'm not familiar with.

    What can I do to reduce false tripping of the GFCI?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 20, 2007, 08:29 PM
    Did the neutral wire from the tub go to the neutral terminal on the GFI breaker, and then connect the breaker pigtail to the neutral bar? This is a typical mistake made.

    If so, ad you have found that these ozonators can cause problems, and if the unit is new then it should be under warranty.

    I am not familiar with the ozonators.

    I also am not sure of what you mean by expensive GFCI disconnect, the 50 amp GFI breaker should be all you need.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Treadmill Tripping Breaker [ 21 Answers ]

We just bought a new mid-range treadmill rated for 11 amps. Our house is relatively new (about 2 years) and the electrical was checked for code by a home inspector when we purchased the house. The treadmill manual stated it was required that it be plugged into a single outlet surge suppressor...

Breaker keeps tripping [ 24 Answers ]

I need to figure this out. I have two 15 amp space heaters in my garage and when I turn them both on it throws the breaker. The breaker at box for this is rated at 20amps. I have been told that I can run both on high and won't throw the breaker. I also replaced the old breaker with a new one (same...

Gfci spa panel tripping [ 4 Answers ]

I just installed a spa with 4 wires. The house is old and while the neutral & ground bus bars are separate in the spa panel, they are all on the same bar in the main panel. Do I need to install a ground rod by the spa panel to keep the gfci from tripping? (instead of running the ground back to the...