    can I run 3 x 2.0 kW panel heaters from a 13 amp circuit safely
    Can I run 3 x 2.0 kW panel heaters from a 13 amp circuit safely
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Oct 22, 2010, 07:25 AM

    What is the voltage that is required?

    For example, a 120VAC/15 amp circuit can only handle a max of 1800 Volt/Amps (or Watts).

    That provides an immediate answer of "No". 2,000 Watts cannot be carried at 15 amps so obviously 13 amp is to small.

    However, a 120VAC/20 amp circuit can carry up to 2400 Volts/Amps (Watts).

    You really need to give us more descriptive information about what you are planning.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Oct 22, 2010, 07:35 AM
    They use 13 amp circuits in the Europe. The voltage is 230 to 240 volts +/-.

    I suspect this is where the poster is from.

    Here is Ohm's Law, plus you will need to confirm any derating values for circuits from your local Building Standards.
    Attached Images
     
    cejames1's Avatar
    cejames1 Posts: 2, Reputation: 1
    New Member
     
    #4

    Oct 22, 2010, 07:40 AM
    Pannel heater installation
    Hi, I want to run three monterey panel heaters as background heat in a small flat, the heaters start at 0.5kW,0.75kW, 1.0kW, 1.5kW and 2.0kW. Is this possible and which ones should I choose please
    I want to just bascally plug them into adjacent existing sockets...
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Oct 22, 2010, 08:48 AM


    I am not familiar with the voltages and amperage's in the UK (I'm guessing that's where you are from), but let's exercise Ohm's Law a little bit. I believe that 3000 Watts or 3.0 kWatts is the max allowed on a 13 Amp circuit.

    0.5 Watts equals 500 Watts. 500/230 (wall outlet voltage?) = 2 amps.

    2.0 KWatts is 2000 Watts using the same principle, 2000/230 = 9 Amps. You cannot use this heater on a 13 Amp general branch circuit with multiple receptacles. Very risky because of its load. It would be fine on a dedicated 13 amp circuit.

    A 1.5 KW heater would require a 7 amp circuit. It would be risky to use this on a 13 amp multiple use circuit.

    1KW will require 4 amps.

    So it looks to me as if you really have three choices. Heaters from 0.5 through 1.0 KW. But I am not really familiar with the standards of UK branch circuits.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Oct 22, 2010, 09:12 AM

    CeJames,

    Please re-read my response. I had to correct some glaring error in it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Tankless water heater installation [ 3 Answers ]

I have seen several tankless water heaters on eBay with Rinnai the only one I know about. I saw Rheem and I assume it will be a reliable model as well. Now to my questions: 1) Has anyone installed a Tankless? Is is too difficult for a amateur handiman? 2) Does anyone know what flow rate you...

Water heater installation kit [ 1 Answers ]

I'm replacing a water heater only I had someone else take it out. I was looking at this kit that has two flexible metal tubing, two 4" compression (?) metal tubes and teflon tape. Should I buy the kit or can I just use cpvc for the cold water intake and metal tubing for the hot water...

Tankless water heater installation [ 8 Answers ]

I'm looking into installing a new tankless water heater for my entire home. I have a 200 amp service, and the unit I'm looking at is 28kw. Would it be better for me to install the 4 30amp two pole breakers that the manufacturer specs. Or should I run a 120 amp into sub panel and then to the 4...

240volt water heater w/ 100 amp service pannel? [ 2 Answers ]

Is it possibble to hook up a 240volt electric water heater when I only have a 100 amp service? It will use 18.8 amps

Block heater- installation [ 3 Answers ]

I posted a question about my car before but can't find it. 89 mustang 2.3 liter won't start when its cold, new battery and iso heat to fuel line still a no go in below zero. I bought a plain block heater, that attaches to the lower radiator hose. Simple enough, I watched my dad replace a broken...


View more questions Search