 |
|
|
 |
Senior Member
|
|
Oct 19, 2010, 03:27 PM
|
|
No ground bar.
"I have an old GE breaker panel (estiamte 70's or later). All of the newer panels I have seen have a seperate ground bar, mine does not. There is a grounding strap from the neutral bar to the box casing. Am I to assume that I can simply ground the circuits I am adding to this neutral bar?"
|
|
 |
Printers & Electronics Expert
|
|
Oct 19, 2010, 06:21 PM
|
|
In panels that old the answer is yes. The Neutral and Ground conductors share the same bus bars.
On current panels the same could be said for Neutral and Ground because the Neutral conductor is bonded (electrically connected) to the metal of the cabinet.
However, bus bars are provided for separate ground conductors and neutral conductors.
If you were to create a sub panel, than Neutral and Ground must be isolated.
|
|
 |
Uber Member
|
|
Oct 19, 2010, 07:07 PM
|
|
Just out of curiosity, Is there a ground wire pulled with each, or did they use the conduits for grounding?
|
|
 |
Uber Member
|
|
Oct 20, 2010, 02:56 AM
|
|
Whether the panel is old or new is not the issue with having separate ground bars.
Any panel that contains the Main Breaker will have the neutral and equipment bar either use the same bar or have two bars be connected together.
Any panel that does not contain the Main Breaker must have the neutrals and equipment grounds separated.
|
|
 |
Printers & Electronics Expert
|
|
Oct 20, 2010, 05:21 AM
|
|
Well TK, you just found yet another problem with my main panel.
The Neutral and Equipment grounds are joined together at the bottom of the panel.
|
|
 |
Uber Member
|
|
Oct 20, 2010, 06:04 AM
|
|
Sorry.
Sounds like you bought a real Money Pit.
I hope you don't use what you see in your home's wiring as an example of how thngs should be done, and give advice based on that.
I keep pounding about where the neutral and equipment ground can be connected, and where not.
|
|
 |
Printers & Electronics Expert
|
|
Oct 20, 2010, 06:34 AM
|
|
No, I use my panel and wiring as how it should not be!
I work very hard at giving advice on what I have learned over the years.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Ground bar and neutral bar
[ 17 Answers ]
I was working on a rehab project, and the guy working on the wiring was installing both the ground wire and the neutral wire together into the ground bar or neutral bar, depending on the side of the circuit.
I was always under the impression that ground wires to ground bar and neutral wires to...
Add Equipment ground bar or remove cross-bar b/w neutrals?
[ 5 Answers ]
I have a GE main breaker load center box in a separate building. It did not come w/ an equipment ground bar. Is it OK to:
1. Remove the cross bar and ground left side neutral to box w/ supplied screw.
2. Attach supplied lug to left side bar and 1/0 ground from SER cable, then all ground...
Connecting Ground bar and neutral bar
[ 6 Answers ]
I'm wiring an additional panel into a garage. It's connected to the Meter through a switch that switches the power between the company power and a generator. The main house panel is inside the house. I understand that the neutral and ground are connected in the "main panel" only and any subpanel...
Ground bar vs. Neutral bar
[ 1 Answers ]
What is the difference? I understand the neutral goes on the neutral bar and the same for the ground wires but if you were to check continuity between the neutral bar and ground bar they are connected. Can you explain?
Ground bar in sub panel
[ 1 Answers ]
Hi,
I want to wire a 240 Volt sub panel in my garage and I have the 2 live wires, the neutral and a ground wire coming in .
In the sub panel, there is a insulated neutral bar and the 2 connectors for the live wires.
There is a little piece of metal with an instruction for grounding which...
View more questions
Search
|