    Required wire for sub-panel, 400 ft, underground, 100 Amp, 120 Volt
    Hello,
    I recently purchased a property which currently has electrical service running into a solitary shed. 400 feet away from the shed is an old foundation I would like to build a cottage on. I'm trying to figure out what it may cost me to run power underground from the shed to the proposed cottage.

    The shed panel box was installed several years ago. I don't know if it's 100, or 200 Amp, but it powers a fridge, well pump, outdoor light, and a couple of receptacles. A trench could be easily dug between the shed and the foundation.

    Using an online calculator I determined that I require 500 mmca aluminum wire to run the distance (120 volt, single phase, 400 ft, 100 Amp). Unfortunately, I know almost nothing about number of conductors, shielding, or running cables underground.

    Does anyone know what wire/shielding would be suitable for this job, and what it might cost?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Sep 16, 2010, 06:00 PM

    Get the power company to move the service closer to where you want to build. Although you can get wire which will handle the load, it won't fit the lugs on 100 or 200 amp CB panel... and it would be very expensive to purchase that wire.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Sep 16, 2010, 06:22 PM

    Also, forget about a 120v feeder or service. This makes absolutely no sense.
    Stick with a 120/240v feeder or service, for several reasons. Wires size and voltage drop being the main ones.
    catfeesh's Avatar
    catfeesh Posts: 2, Reputation: 1
    New Member
     
    #4

    Sep 17, 2010, 06:18 AM
    Comment on Missouri Bound's post
    I was afraid of that answer, the cost of moving the service would likely negate the cost benefit of using the old foundation. Thanks for the helpful information.
    Muskwa's Avatar
    Muskwa Posts: 2, Reputation: 1
    New Member
     
    #5

    May 22, 2012, 11:33 AM
    I want to feed a 3phase 100 amp panel 120/208v which is 400 ft. Away. I then want to feed another panel (100amp 3 phase) from that first panel which will have a load of 60 amps. One of those loads is 200 ft away 3phase 30 amps. What wire sizes do I need to feed these panels and load.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    May 22, 2012, 01:46 PM
    Quote Originally Posted by Muskwa View Post
    I want to feed a 3phase 100 amp panel 120/208v which is 400 ft. Away. I then want to feed another panel (100amp 3 phase) from that first panel which will have a load of 60 amps. One of those loads is 200 ft away 3phase 30 amps. What wire sizes do I need to feed these panels and load.
    A) This should be in it's own thread. This has nothing to do with the original post.

    B) Your electrician will know exactly how to do this. This is not a DIY project and anyone who has to come to a DIY message board to ask how should not be doing it!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire UF wire to run to new 100 amp service panel? [ 10 Answers ]

My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is...

240/120 volt single phase (80 amp load) underground 180 feet [ 1 Answers ]

What is the recommended wire size to allow the use of either 2 hp radial arm saw or a stick welder plus 20 amp continuous lighting load.

Wire size for a 100 amp lug sub panel [ 4 Answers ]

Hi I have a 200 amp main panel, but it is a small 24 slot panel. It is full and I need to add three more circuits. I want to run a 100 amp main lug subpanel. The plan is to move the clothes dryer breakers to the new sub and use the existing location in the main panel to install a 100amp breaker...

Wire needed for a 100 amp sub panel? [ 3 Answers ]

I am installing a 125 Amp Sub panel in a detached shed approximately 100' from the house. The subpanel has a 100 amp main breaker in it and I have a 100 amp breaker that will go in the main house panel to feed it. I will be using #4 copper THHN for my 2 hot conductors and neutral conductor and a #6...

100 amp sub panel wire size [ 2 Answers ]