    Ground and neutral shorting
    What will happen if the ground wire and neutral wire shorted?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 7, 2010, 05:04 AM
    On a normal circuit, nothing should happen that you can see or be aware of.

    On a GFI protected circuit, the GFI will trip.

    This condition, when known, needs to be corrected, as the neutral is current carrying, and a neutral ground short will send current through the grounding system. Arcing can happen at loose connections of the grounding system, even thou there should be no loose connections, it still happens.
    mixa.srbin's Avatar
    mixa.srbin Posts: 32, Reputation: 3
    Junior Member
     
    #3

    Oct 7, 2010, 06:09 AM
    Hi, if ground wire and neutral wire shorted nothing will happen. Neutral wire is actually a ground from the electric substation. Ground wire in your house is used as a replacement for neutral wire in case of it's breaking, to provide grounding in order to prevent your home appliances from burning out. So, if you connect ground and ground nothing will happen.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 7, 2010, 07:03 AM
    In North America, this statement is NOT TRUE:

    Quote Originally Posted by mixa.srbin View Post
    Ground wire in your house is used as a replacement for neutral wire in case of it's breaking, to provide grounding in order to prevent your home appliances from burning out. .
    A neutral is a grounded return for the circuit, and is to be kept separate from equipment grounding in circuitry.

    An equipment ground, green, bare, or green with yellow stripes, is only to ground the metal raceway and metal housing of an appliance.
    nithin111's Avatar
    nithin111 Posts: 3, Reputation: 1
    New Member
     
    #5

    Oct 9, 2010, 11:13 PM
    Comment on tkrussell's post
    There is a continuety between the Neutral and Ground of the DG in my factory(in both input and Output side). Is there any problem because of that? If so what type of preventive measures should I take?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Oct 10, 2010, 03:55 AM
    There will be continuity between neutral and ground, as they are joined at the mains service disconnect.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Neutral wire used as a ground? [ 3 Answers ]

I have been changing switches and plugs and in one of the receptical boxes I found the neutral wire pigtailed to the side of the box, and when I installed the new receptical there was no circuit until I did the same, pigtailed to the box... is this safe?:confused:

Neutral / Ground [ 3 Answers ]

OK Strat, Here is the photo clip of the schematic of the Neutral /Grounding system in my place. Don

Open ground when neutral not touching ground [ 3 Answers ]

Hi, I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to. It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...

Ground and neutral bar [ 2 Answers ]

I'm installing a 4 wire, 50 AMP GFCI for my hot tub. My question is at my main breaker for the house where I'm taking power from, which bar is neutral and which bar is ground, or does it matter? Thanks Fred

Using Neutral as a Ground ? [ 3 Answers ]

In my new apartment there are some wall outlets that are two prong outlets. Also my fear is that the three prong outlets are not “physically” connected to ground. I heard somewhere that in this kind of system the neutral wire can also be used as a ground. Is this correct? Would a separate...


View more questions Search