    Hot Tub (spa) GFCI Wiring
    We have a ThermoSpa Hot Tub outside on our deck that came with the house (in MA). It requires 2 - 240v circuits, both 30 amps. It is currently wired with the following:

    Main (house) Panel:
    1 - 30 Amp 240V GFCI
    1 - 20 Amp 120V GFCI (incorrect, need a 240v)

    Sub-Panel near Hot Tub, outside:
    -Hard wired with a "big handle" type switch on the side, no additional GFCI, controls ONLY the 240V line.

    They originally hijacked the 240v supply for the Range, and added a GFCI breaker, but they did NOT connect the White load-wire to the GFCI and left it connected to the neutral\ground bar in the box (which I fixed). They did the same thing for the 120v GFCI breaker, so I moved the white wire to the breaker for that one as well. The white pigtails were connected to the ground strip on both GFCI breakers. (I hope all that makes sense!)

    My questions are:
    1) Is it OK that the GFCI breakers are in the main box?
    2) is it OK that there are no breakers in the Sub-Panel and just a large lever-type switch?
    3) Am I correct that all load-wires should be connected to the GFCI breaker (red, black, white), except for the ground wire?
    4) Is there any way to test the GFCI breaker other than hitting the "TEST" button (ie, short out the line at the Hot Tub)

    Thanks for your help!
    Dr_Spa's Avatar
    Dr_Spa Posts: 101, Reputation: 13
    Junior Member
     
    #2

    Oct 4, 2010, 02:37 PM

    Yes
    Yes (as long as it breaks every hot wire)
    Yes
    Yes (though this is a rather expensive piece of test equipment)
    volk1's Avatar
    volk1 Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 5, 2010, 06:17 AM
    Thanks for your help!

    One last question: They used aluminum wire (appears to be very heavy gauge) on the 30 Amp 240V line to the Hot Tub. Will that be OK? The hot tub does say "copper only." Should we look to replace this when possible?

    Thanks!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

Wiring SPA/Hot tub [ 18 Answers ]

I am contemplating installing a SPA on my back patio slab. My 150 ampere panel is about 100 ft away. My plan is to run 6/3 along my outside eave (does this need to be in conduit?) and down an outside wall to the sub panel, because I live on a slab and do not have any other choice. My dilemma is...

Hot Tub Wiring - GFCI [ 1 Answers ]

I have a hot tub currently wired at my home in the following configuration: 50amp breaker at the main panel to 50 amp GFCI breaker mounted outside, on the house near tub to Spa main panel inside tub which has a 110v GFCI module. My issue is that sometimes when I kick on the heater while the...

Square D Company spa hot tub breaker 50 amp gfci [ 1 Answers ]

I am trying to connect the wires from the hot tub to the braker, but can not take the braker out of the box. It will pop out on the top but still can not take the whole braker out to connect all the wires, special the white one which goes close to back of the braker.

Items for Wiring 220v Spa/Hot Tub [ 5 Answers ]

I need to know what type of wire to use for wiring a 220v hot tub. The breaker box is in the house, the wire will come through a concrete wall.


View more questions Search