240v transformer to 120,208,240v what wires
[ 3 Answers ]
I'm replacing a 240v transformer in a split heat/cooling unit. The old trans has 4 prongs 2 load 2 line the new one has two secondary and 4 primary wires what wires do I use for primary?
240v basebord heater, and breakers
[ 1 Answers ]
I have 2-8ft 2000 watt (8.3 amps each, total 16.6 amps) heaters wired to a 20 amp breaker with no problems. But since each of the heaters are in different rooms, and one room is bigger (where the thermastat is) I need to change this one baseboard to a 2500 watt 8 ft 10.1 amp unit to equal out the...
Single pole breakers for 240v heater?
[ 2 Answers ]
Thanks in advance for any help.. I am trying to set up new 240 v baseboard heating in my attic My questions is can I put it through 2 different single pole breakers - each for every phase? Heater = 240v / 1500w breakers = 15A And what can be wrong? (technically - this is not a code...
82v on one leg of 240v at breaker box
[ 1 Answers ]
Neighbor complained of 120v window A/C not working and dim lamps on same circuit in old mobile home. Check of circuit revealed 82v on 120v circuit. Further check of incoming line showed 82v on one leg of service in breaker box (resulting in 82v on the affected bus bar). Disconnect box at service...
Connecting 240v heater to 2 - 1 pole breakers
[ 2 Answers ]
I have 2 - 15amp tandem breakers - both are 1 pole. I know that normally you would use a 2 pole breaker to create a 240v feed to the heater. However, if I connect my 12-2 wire to the 2 different breakers, I get 240v and my heater works correctly. Is there any problem to doing this rather than... View more questions Search
|