I have a Generac Guardian 7kw standby generator. It is set up to operator on natural gas. It won't start in auto or manual mode. The engine doesn't crank. The starter solenoid just makes a chattering sound but doesn't engage the starter. Thinking that the solenoid was bad, I bought a new solenoid and it does the same thing. The control wiring on the solenoid has about 6.5 volts when it is trying to engage to start. Does anyone have a suggestion about where to go from here in trying to diagnose the problem? Thanks
|
|
 |
Home Improvement & Construction Expert
|
|
Aug 31, 2010, 01:15 PM
|
|
Does the chattering come from the solenoid or from the starter?
|
|
 |
Ultra Member
|
|
Aug 31, 2010, 03:42 PM
|
|
Did you check voltage in the battery,
|
|
 |
New Member
|
|
Sep 2, 2010, 03:48 PM
|
|
 Originally Posted by hkstroud
Does the chattering come from the solenoid or from the starter?
Harold, the chattering is coming from the solenoid.
|
|
 |
New Member
|
|
Sep 2, 2010, 03:50 PM
|
|
DG, I checked the battery voltage and it is fine... 14 volts. Thanks for any help.
|
|
 |
New Member
|
|
Sep 2, 2010, 03:53 PM
|
|
I haven't had a chance to reply or work on the problem the last day or so, but I'm going to try to get to it tomorrow. Would like to get it running in case of the need due to bad weather. We live in south Alabama and there is always the danger of hurricanes this time of year.
|
|
 |
Home Improvement & Construction Expert
|
|
Sep 2, 2010, 07:24 PM
|
|
Check all connections and wire of control wires. Amperage of control wire would be low but voltage should be 12 volts.
|
|
 |
New Member
|
|
Sep 3, 2010, 08:12 AM
|
|
Ok, I checked all connections and found one. Fixed it but that wasn't the problem. It is an intermittent problem though. Traced the wiring from the solenoid to the circuit board. At first I had only 6 or 7 volts when trying to start and then for a minute I had about 13volts. I hooked the solenoid back up and tried it again but the voltage was back to 6. I'm thinking the circuit board is bad. Its getting 13 to 14 v from the battery but isn't sending but 6 or 7 down to the solenoid when it is energized.
|
|
 |
Ultra Member
|
|
Sep 3, 2010, 07:14 PM
|
|
If your in a spot and need it , you can run a hot wire from the switch to the solenoid and by pass the board until you get one.
|
|
 |
New Member
|
|
Sep 5, 2010, 05:13 PM
|
|
Ok, finally got around to working on my problem again. Looks like it simply going to be a defective battery. Yeah, I checked the voltage and it was fine. Just a normal 12v battery. But when you hit the start switch and try to start, the voltage at the battery drops to about 6 volts. So I jumped it off and it works fine. Currently charging the battery to see if it will operate the generator, if not then I'll be buying a new battery. I never have seen a battery's voltage drop. I thought it was either 12v or not like with a dead cell.
|
|
 |
Ultra Member
|
|
Sep 5, 2010, 06:44 PM
|
|
Good job.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
What rights does a standby guardian have?
[ 3 Answers ]
My brother is developmentally disabled. Our mother is his legal guardian. I am listed as a standby guardian on the guardianship papers. Mom is 88 and in an assisted living facility. Do I have the legal right (as standby) to make decisions, sign papers etc or do I have no power while Mom is...
Standby generator
[ 7 Answers ]
After a recent ice storm and power outage, I have begun looking into installing a standby generator for my important items in the event of a power failure. Anyone have experience with these devices? Anyone have any recommendations or feedback from personal experience? I'm open to suggestions and...
Size of Standby Electrical Generator
[ 3 Answers ]
I have a 2000 sq ft house, with air conditioning, swimming pool circulation equipment and normal lighting, ceiling fans etc. The breaker panel is rated at 200 AMPS. I want to have a standby back-up electrical generator that will have enough power to run the A/C, pool, range, and normal lighting,...
Furnace shuts down standby generator
[ 7 Answers ]
I have installed a 16kW standby generator and I am having a problem with the furnace. It is a 10kW furnace and the rest of the generatoris running lights, outlets and a well pump. When the generator starts, everything is fine. Then about five minutes with the generator running, it trips the 65 Amp...
Generator for the house, Guardian?
[ 3 Answers ]
Hello all,
I asked this question a long time ago, but it seems that I'm finally going to give in and buy one. I thought I could get away with just a portable generator, but after Wilma blew through South Florida, my house will not have power back until November 15th. Luckily, the weather is...
View more questions
Search
|