Ask Experts Questions for FREE Help !
Ask
    Snowman316's Avatar
    Snowman316 Posts: 1, Reputation: 1
    New Member
     
    #1

    Aug 21, 2010, 12:04 PM
    Voltage between the ground and neutral
    I am getting a reading of 50 volts between ground and neutral, and ground and hot. In the j-box where the 12-2 romex is connected to the hot and neutral. I disconnected the ground wire in the romex completely. The ground is not touching the j-box or anything else. On the other end of the same romex that feeds a ceiling light I disconnected the ground completely. At that ceiling box I am getting a reading of 120 volts from neutral to hot. When I go from ground to neutral I get 50 volts. And when I go from ground to hot I get 50 volts. Both ends of the ground wire are completely disconnected. Also, I traced the 12-2 romex from the jbox to the ceiling box and there is not a jbox between the two boxes. The 12-2 is laying in the attic exposed and appears not to be damaged. Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 22, 2010, 06:18 AM
    Sounds like you have done all that is possible to isolate this ground wire in this cable, it is disconnected at both ends, and no other splices in this cable, completely isolated and located.

    To start and help locate the source of this voltage, try shutting off each circuit breaker to determine what circuit, if any, the source of this voltage is. May not be relevant, but good place to start.

    If any one breaker does not cause the voltage to go off, shut off all breakers, including the main.

    If you can eliminate the voltage, then try doing a continuity test between the ground wire and a known ground, preferably a water line. There should be no measurement.

    Can you see the entire length of this cable?

    Any chance it is shorted to a water line, or some other grounded system?

    Need to try these tests before moving on.

    This all assumes you are using a good quality voltage meter.

    Sometimes, voltage is induced in a conductor because it runs near a live source.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Aug 22, 2010, 06:23 AM

    Sorry but my first thought is, are you sure you have your meter set correctly? An ac circuit will induce a small voltage in an unconnected conductor that runs parallel to other conductors. Perhaps your meter is set to dc volts..

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Voltage on the neutral [ 1 Answers ]

With the breaker on said circuit live and active, I noticed the neutral for that circuit was loose. Took it out from its termination screw to check it for corrosion and it sparked. Put my meter across the said neutral and the ground lug and was getting a voltage reading of 120ish. This so far...

Voltage on the neutral - How? Why? [ 4 Answers ]

Hello all, I've run into a "situation" I'd like advice on. The job was simply replacing an outlet. Inside the outlet box are 2 12/2 cables with ground. The outlet is a standard 110V, and the top and bottom receptacles are connected (in other words, it has not been severed to form...

Low voltage between Ground and Neutral [ 1 Answers ]

I am new to this forum and this is my first question. Should a properly wired 110 Volt house circuit have measurable or any voltage at all between the Neutral and Ground wires? Please advise if more specifics are required for a complete answer. Thank you, Bernard

Voltage on neutral [ 3 Answers ]

I just ran a completely new 10 gauge wire for my newly relocated clothes dryer. I wired up the breaker and turned if off, and turned the main breaker back on. When I measure voltage between the black and white OR between the red and white even though the breaker is OFF I get 1.3 volts. How...

Open ground when neutral not touching ground [ 3 Answers ]

Hi, I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to. It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...


View more questions Search