    Replacing HH84AA011 with icm271
    The blower runs continuously after the new board install. I did some checking with my volt meter and here is what I have.

    On the low voltage block
    R - 24v
    GH - 24v
    C - is grounded

    On the rest
    PR 1 - 0
    L1 - 120
    L2 - 0
    PR2 - 0
    Com - 0
    LO - 120
    HI - 0
    Gas1 - 0
    Gas1 - 0
    Gas1 - 0
    LIM1 - 26
    LIM2 - 24
    Sec1 - 26
    Sec2 - 0

    Any Idea what is tripping the blower? Also is there anywhere that I could find out what all of these abbreviations are so I know for future reference?
    Thanks in advance.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    May 6, 2010, 06:46 PM
    Has the tstat been ruled out? Are you setting it on auto? Not fan,, most people hate getting this question,but,not being there all possibilitys have to be checked out,, have you disconnected the tstat wires from the furnace? And does it still run continuously ?
    Onefastdak's Avatar
    Onefastdak Posts: 2, Reputation: 1
    New Member
     
    #3

    May 6, 2010, 06:52 PM

    I tried disconnecting all of the thermostat wires and it still runs continuously. There is also a test jumper on the new board so I tried that also.
    dank1j's Avatar
    dank1j Posts: 4, Reputation: 1
    New Member
     
    #4

    Aug 1, 2010, 02:25 PM

    Having similar issues with a 302075-302 replacement.
    Initial problem was constant fan on even with t-stat off.
    But A/C would work.

    Now A/C does not work (compressor won't come on) and no
    Cool air and internal fan runs continuously.
    No voltage R-C
    30 VAC across sec-1 and sec-2 which is high.

    The fuse seems to be fine and the limit switch and fuseable link seem to be fine.

    Thanks for any help.
    dank1j's Avatar
    dank1j Posts: 4, Reputation: 1
    New Member
     
    #5

    Aug 1, 2010, 07:08 PM
    Quote Originally Posted by dank1j View Post
    having similar issues with a 302075-302 replacement.
    initial problem was constant fan on even with t-stat off.
    But A/C would work.

    Now A/C does not work (compressor won't come on) and no
    cool air and internal fan runs continuously.
    No voltage R-C
    30 VAC across sec-1 and sec-2 which is high.

    The fuse seems to be fine and the limit switch and fuseable link seem to be fine.

    thanks for any help.
    This guy (me) doesn't know what he's doing.
    The fuse was blown and it blew again on a new one.
    Replaced with a 5A fuse (not 3A) and it is working for now.

    If no other ideas come in, I'll order the transformer and
    Put the 3A fuse back in to test.

    Any help is appreciated.
    Thanks.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #6

    Aug 1, 2010, 08:08 PM

    (quote)If no other ideas come in, I'll order the transformer and
    Put the 3A fuse back in to test.

    Not sure why you wanting to replace transformer
    If the transformer was bad,seems to me nothing would be working
    Sounds like a low voltage short,either the wiring or bad contactor
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Aug 1, 2010, 09:16 PM

    Probably JW-1 needs to be cut/removed.

    See: http://www.icmcontrols.com/downloads/icm271_ag.pdf
    dank1j's Avatar
    dank1j Posts: 4, Reputation: 1
    New Member
     
    #8

    Aug 8, 2010, 03:35 PM
    Quote Originally Posted by KISS View Post
    Probably JW-1 needs to be cut/removed.

    See: http://www.icmcontrols.com/downloads/icm271_ag.pdf
    Cutting jw1 doesn't seem right:
    2. If the JW1 jumper is cut, a constant low-speed blower will occur without any thermostat signal. Also, a signal applied to the GC or Y terminals will not bring on the hi-speed blower during the cooling mode. Therefore, the JW1 jumper must not be cut on cooling applications.
    Thanks.
    dank1j's Avatar
    dank1j Posts: 4, Reputation: 1
    New Member
     
    #9

    Aug 8, 2010, 04:11 PM
    Quote Originally Posted by wmproop View Post
    (quote)If no other ideas come in, I'll order the transformer and
    put the 3A fuse back in to test.

    not sure why you wanting to replace transformer
    if the transformer was bad,seems to me nothing would be working
    sounds like a low voltage short,either the wiring or bad contactor
    Thanks for the help. It is appreciated.
    Well I got the transformer in and will try to install later today.

    So, we'll know more then. If a short is the problem wouldn't the
    5A fuse blow as well? It worked for an hour long test w/ the 5A in
    And the 3A blows almost immediately.

    The old transformer might always have run at 30V on the SEC and the old board didn't have the fuse to blow. I don't have the knowledge to calculate the 24 v 30 V difference in current, so I don't know for sure that it would blow the 3A but not the 5A.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #10

    Aug 8, 2010, 04:15 PM

    Good point!

    From the mnual:

    If the old Carrier/BDP unit has (2) black relays just like the ICM271, then look for the JW1 jumper and R17 resistor on the Carrier/BDP board. They will be in the same location as the JW1 and R17 on the ICM271. If either one (JW1 or R17) has been cut, then cut the ICM271 equivalent. This will match the original Carrier/BDP blower speed option.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing GE Honeywell Weathertron and Replacing with Hunter Model 44860 [ 1 Answers ]

I need help... I am having furnace problems and I'm hoping changing the thermostat may help. But the Hunter wire diagram letters do not match that on the Honeywell. The letters on the Honeywell are R, T, O, G, Y, X2, B AND W. The wires on the Hunter are RC/R.C.Y1, Y2,W2,L,E,O,B,G.

ICM271 rplcm'nt for HH84AA [ 7 Answers ]

My PDB ( Payne Daynight Bryant ) furnace is a model 396GAW. I recently replaced the fan control circuit board because the ice cube relay was hanging up, and not releasing, allowing the fan to run continuously. I was able to nurse it through a season by cleaning and polishing the contact, but...

Connecting Honeywell RTH230B to ICM271 [ 1 Answers ]

I hooked up our new Honeywell RTH230B last fall and it worked fine, but now we get no ac when we turn to cooling. The fan comes on in the house, but the outside unit does not turn on. I can push the relay in (on the outside unit) and the cooling unit works as long as I have it held down. I have...

Does replacing outside A/C unit require replacing inside unit [ 2 Answers ]

I have a 10 year old 10SEER Trane outside and inside unit. The coil is leaking freon in a few spots. The first technician gave me a quote to replace the outside and inside air handler with a 13SEER for around $4800. The second technician I called came out and suggested only replacing the outside...

ICM271 Carrier Replacement board Fuse blows [ 4 Answers ]

My Furnace recently stopped working and the Furnace Fan stayed on constantly. I replaced the original Fan Control circuit board (HH84AA011) with a ICM271 drop in replacement board. Still nothing came on, not even the constant fan. I check the 120V-24V transformer and found no 24V output so I...


View more questions Search