    My mcb switch keeps on tripping.. tried all the ways possible...
    As I have said.. my mcb switch keeps on tripping.. tried all the ways.. removed all appliances... changed even the mcb.. any more suggestions.. its only one room of my house that is giving the problem it's a 10A mcb... need help guys.. please... its really irritating... help please...
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 3, 2010, 02:49 AM
    A loose connection can cause heat, even with a 10 amp load, and cause the CB to trip.
    I had one customer that had a 20, (twenty) amp load tripping a 200, Two hundred, amp MCB, all because of a loose nut bolting the breaker tab to the panel bus bar.

    I was only able to find it using infrared detector.

    Or the MCB is defective.

    Changing a Main Breaker requires the help of a professional. And often the utility is needed as they do not allow electrician to pull the utility meter. Some do, some don't

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What's the difference between ac mcb and dc mcb and shall I use the ac mcb for DC [ 1 Answers ]

What's the difference between ac mcb and dc mcb and shall I use the ac mcb for DC?

Safety switch keeps tripping [ 4 Answers ]

I have a Carrier unit with a Becket Model "AFG" oil burner. Unit was installed 5/2002. It was given its maintenance service on 11/15/07 by Carroll Ind. I was delivered 100 gal of oil the week before Christmas around the 18th. System has been working fine until 2 weeks ago when the Honeywell...

Tripping of ac mcb on dc current below its rated current [ 2 Answers ]

Please let me know why ? MCB rated for 240/415VAC, 6Amperes trips on 5 Amps DC current at 24VDC voltage level Ambient operating temperature: 32 ° C MCB Designed for ambient temperature of 55° C Why MCB should trip:confused: ?


View more questions Search