    Can 20 amp mini breakers be used on electric heaters
    Can 20 amp mini breakers be used on electric heaters
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #2

    Jun 30, 2010, 02:54 PM

    If heater calls for 20 amp breaker, yes.

    A 20 amp breaker or mini 20 amp both operate the same, just gives u more room for circuits in panel box.

    Chuck
    burtonb's Avatar
    burtonb Posts: 3, Reputation: 1
    New Member
     
    #3

    Jun 30, 2010, 03:00 PM
    Had 110 both sides and it wouldn't work! Put in standard size 20 dble and it worked!
    I am stumped!
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Jun 30, 2010, 05:27 PM
    A "mini-breaker" that you describe isn't 2 pole... it's a single pole breaker with two switches. You can't get 240 volts from that. It's 2 120 volt circuits on the same leg.
    burtonb's Avatar
    burtonb Posts: 3, Reputation: 1
    New Member
     
    #5

    Jun 30, 2010, 08:41 PM
    Comment on Missouri Bound's post
    Damn do I feel stupid!! Thank ypo.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jul 1, 2010, 12:40 PM
    If your breaker is similar to the one in the photo, a 2 pole half size breaker with the two handles tied together, this one difficlut to see the pin in between the handles, then it is the correct breaker, you just had in in the panel incorrectly, both poles on one leg of the panel.

    A full size two pole breaker is fool proof, it will only install so that each pole connect to each leg of the panel.

    The label on the half size breaker, if truly is correct, will state 120/240 volts, and somewhere on the breaker it will state "common trip".
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cambridge electric heaters electric use cost [ 1 Answers ]

How much does it cost too run heater?

Electric amp breakers [ 1 Answers ]

Can I put a thirty amp bresaker on a 50 amp line to attach a 30 amp oven?

Electric Breakers [ 1 Answers ]

I have a Square D breaker 150 panel box in my home. I wanted to put in a double breaker (20 - 20) but they don't make one for my particular box (it doesn't push in far enough to put the cover on). The guy at the store suggested I file out some of the matterial on the breaker so it pushes in all the...