    10 seer condenser and 13 seer evaporator
    If you put a new 13 seer fan coil in a system and keep the 10 seer condencer outside will this still balance out or will it cause execive compresser wear and cause a burn out?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jun 19, 2010, 09:47 PM
    You can do that but I recommend the use of an expansion valve with a hard start kit and a time delay os some sort on the low voltage signal source for the outside unit.

    It is hard to get a good match with a piston with that combo so that is why I suggested expansion valve.
    barcooler's Avatar
    barcooler Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 20, 2010, 06:28 AM

    The new coil has a txv and I quickly found a hard start was needed the unit ran for a few more days but jusy would not cool the space so they shut it down. When I checked the unit I had uwards of 35 degrees of superheat and no subcooling at all. I closed the liquid line valve to see how far down the compresser would pull, and found it would not break 0. I conclude the valves are not holding. I am still wondering if the mismatched seer ratings of the fan coil and the condencer had was the cause of this. Now there are other issues here I have not yet run a load calc on this room, it is a kitchen and I am not sure it was sized properly to begin with. I know the seer is a ratio of cooling over watts but do they not in part make these gains by altering coil sizes. There
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jun 20, 2010, 08:40 AM
    Quote Originally Posted by barcooler View Post
    the new coil has a txv and i quickly found a hard start was needed the unit ran for a few more days but jusy would not cool the space so they shut it down. when I checked the unit I had uwards of 35 degrees of superheat and no subcooling at all. I closed the liquid line valve to see how far down the compresser would pull, and found it would not break 0. I conclude the valves are not holding. I am still wondering if the mismatched seer ratings of the fan coil and the condencer had was the cause of this. Now there are other issues here I have not yet run a load calc on this room, it is a kitchen and I am not sure it was sized properly to begin with. I know the seer is a ratio of cooling over watts but do they not in part make these gains by altering coil sizes. there

    If the coil came with a TXV was it for the correct refrigerant R-22 or R-410A?

    If the unit was overcharged it is possible it will not be able to pump all the refrigerant down into the condenser.

    If the unit was overcharged it is possible liquid flood back damaged the compressor valves.

    If it is a commercial kitchen remember that air makeup might be needed to compensate for the range hood exhaust if so equipped and that will play a part in your calculations. Also remember to calculate the appliance heat gain and moisture discharge from the cooking.

    A properly cooled kitchen will take a boat load of cooling BTU's and most companys usually do not really cool the kitchen but use the unit as a large dehumidifier since utility costs are so high.

    Good luck.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can uReplace a 10 seer ac condenser w/a 13 seer w/o changing the inside 10 seer unit [ 8 Answers ]

We have a 10 seer 2.5 ton heat pump outside condensing ac unit, that sprung a leak that cannot be repaired. We have had 5 repairmen come out and look. 3 of them say we have to replace the inside 10 seer 2.5 ton compressor and furnace as well. 1 of the 5 says we can just replace the outside unit...

AC Question: How large of a SEER condenser... [ 1 Answers ]

How large a SEER condenser will 120' of 5'16" verticle copper tubing on a split system (condo-live on 1st of 12 floors) effectively handle? I don't have the option to change to 3/8" line. I currently have a 2 ton Trane 11Seer and want to upgrade to a 2 1/2 ton Trane, ideally 16 SEER.

2 story 4000 sq ft house. Is a 14 seer better than 16 seer [ 1 Answers ]

2 story 4000 sq ft house. I have a choice of 14 seer or 16 seer. Which should I go with?

14 SEER vs 15 SEER Trane Heat Pump [ 2 Answers ]

I received two quotes for a 14 and a 15 SEER Trane R410A heat pump. The price difference was $2900 between the two quotes (there's duct work $$ in the quote as I am doing a major remodel and adding lots of new space) The question is should I ave the $2900 or does the extra efficieny pay off? ...

Air handler seer 10? WIll it be OK with a seer 13 heat pump. [ 1 Answers ]

We are replacing our old heat pump... the air handler was replaced 4 years ago and is good condition. Everyone wants us to replace our hole unit and we really don't want to put out that much $$ at this time. Can we just replace the Heat pump? Or do we have to replace both. Everyone says they...


View more questions Search