    How to calculate the dc short circuit current for a dc system
    I have a battery string of 60 single cell batteries making up our 125VDC main station service for our power plant. Each battery is rated as follows:
    Lead-calcium type storage batteries, Exide F, FTC-15 , Cat. no. 73336, Nominal capacity 1180AmpHr, 1.205-1.220 specific gravity at 25 degrees Celsius (77 degrees Farenheit). They were manufactured on 1/12/1988.
    How do I calculate the DC short circuit current from this source ?
    InfoJunkie4Life's Avatar
    InfoJunkie4Life Posts: 1,409, Reputation: 81
    Ultra Member
     
    #2

    Jun 3, 2010, 05:51 PM

    In what configuration are they connected. All series, some series some parallel?

    I'm not sure what you mean by short circuit current, someone else here may. I know you calculate dc loads and such by using the following equations.

    P=EI

    and

    E=IR

    E = Voltage (In Volts)
    P = Power (In Watts)
    R = Resistance (In Ohms)
    I = Amperage (In Amps)

    Good Luck...
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jun 3, 2010, 06:45 PM

    You need to find the ESR of a battery and add them up. ESR is a good way to determine the health of a battery. ESR is the Effective Series Resistance.

    The manufacture would know this and if you had the spec of Cold Cranking Amps, you can generally back out ESR.

    Your sort of looking for the slope when the battery is heavily loaded.

    Battery testers can run an I-V on the battery or they can just do it with a load.
    Zog's Avatar
    Zog Posts: 7, Reputation: 1
    New Member
     
    #4

    Jun 8, 2010, 10:02 AM

    Best way is to use the DC module in SKM.

    Or measure the battery bank Impedance (Meggers EBITE tester will do this), Isc will be Vt/Z

    Or for a good guestimate, the Isc will be 20x the 3hr discharge rate, if you do not need an exact number this works fine.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to calculate the short time current rating for current transformer? [ 4 Answers ]

Respected sir's, Please clear my doubts? How to calculate the "short time current rating"(i.e-primary short time current rating-like if u take 400-400/5-15va/class1,40ka/3sec). 40ka/3sec-how to calculate this rating from the substation? Is there any formula?please advise me... ...

How to calculate the short circuit current flow in a three phase circuit [ 3 Answers ]

How to calculate the short circuit current flow in a three phase circuit?

Short circuit current calculation in dc system [ 0 Answers ]

How do we calculate short circuit current in dc system?

Current transformer - short time withstand current [ 4 Answers ]

Hi, For ring-type (window-type) CT, do we need to size the CT short time withstand current at the same or above the system short time withstand current (short circuit level)? Any reference/technical explanation? Thanks!

Short circuit current fault [ 1 Answers ]

I have quite a simple system. Contains one substation, feeder pillar and 3 houses. I have calculated the short circuit current that the transfromer in the substation can deliver but is there any one that can help me with finding the equations to calculate the short circuit current level supplied by...


View more questions Search