Ask Experts Questions for FREE Help !
Ask
    adam3432's Avatar
    adam3432 Posts: 1, Reputation: 1
    New Member
     
    #1

    May 28, 2010, 08:46 AM
    Trouble with Wiring Dual light switch Celing fan
    I am having trouble wiring my Dual Light Switch Celing Fan. From the Outlet Box on the Left side I Have Copper, Red, Black, White Wiring. On the Right Side of the Outlet Box I have Black, White and Copper Wiring. From the Fan I Have Blue,White, Black, and Green.

    Can Somebody tell me what wires I should hook up from the fan to the Outlet Box?
    WallyHelps's Avatar
    WallyHelps Posts: 1,018, Reputation: 136
    Ultra Member
     
    #2

    May 28, 2010, 03:10 PM

    What wires do you have in the ceiling where the fan connects? I'm assuming Black, White, Red, Copper in my comments below.

    First, see if you have power on the Right side of your outlet box (the Black, White, Copper set). I'm going to assume you do (between black and white). Now, turn off the power at the breaker panel!

    The drawing shows what I'd do:
    1. Connect Ground Wires
      The bare copper wires get connected to the green screws on the switches. You'll need a short piece of bare wire to run between the switches. Don't make it too short. 5 inches should be good.
    2. Connect Neutral Wires
      Connect the two white wires together with a wire nut
    3. Connect Hot Wires
      You'll need a short piece of black wire to run between the switches, again about 5 inches should work. Then run the black wire from the supply (right side in the drawing) to the closest switch screw that the short black wire is connected to. (You might want to use the push-in connection on the back of the switch for the short wire).
    4. Connect Switched Wires
      Now connect the remaining two wires--one to each to the empty screws on the switches.
    5. Connect Fan Wires
      At the ceiling connection, hook up as follows:
      • White to White
      • Black to Black
      • Red to Blue
      • Bare Copper to Green


    Turn the power back on and check to see if one switch controls the light and one controls the fan (you may have to pull the chains on the fan itself to get those in the "on" position).

    Remember that if the assumptions I mentioned above are not correct then my procedure will most likely not work either (and could be dangerous).

    Best of luck,
    WallyH

    P.S. I re-read your problem description and now am uncertain if you needed help with the switch wiring or just the fan connections. If the switch box is already wired up, then just do the "Connect Fan Wires" portion of the procedure above.

    P.P.S. Be sure to read and understand Don's answer below. What he describes is another way your wiring was done (and probably the more common way, in fact). Just closely examine what you have to begin with to figure out how things are arranged. Post back with what you learn if it isn't perfectly clear.
    Attached Images
     
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    May 28, 2010, 06:48 PM

    Adam,

    Please read this prior to doing the work.

    What you are describing is a "Switch Loop" being fed from the ceiling feeder.

    On the black and white from the supply, you should find 120 VAC.

    That white wire is the "grounded Conductor" also know as "Neutral".

    The Second white wire (the one in the cable going to the switch outlet box, that is a White conductor is actually being used as the Hot Feeder to the switches.

    There should be either black tape or black ink (from a sharpie pen) on both ends of the white conductor to signify the re-tasked conductor. At the switch outlet box, you should find the white wire spliced together with two black conductors (called a pig tail) each black conductor going to the bottom of each switch. One switch will have a black conductor returning power to the ceiling and the other will have the red conductor returning power to the ceiling.

    At the ceiling box, I would expect to find the black from the switch connected to the Black on the fan. The red from the switch would normally connect to the Blue from the light package. The white from the fan, connects to the white from the ceiling feed pair.

    The bare ground in the ceiling will connect to the green conductor from the fan and the bare wires from the ceiling and the switches.

    I'd do a graphic for you if I wasn't so terrible at them.
    ceilingfanrepair's Avatar
    ceilingfanrepair Posts: 5,733, Reputation: 109
    Uber Member
     
    #4

    Jun 22, 2010, 12:37 AM

    Don is most likely correct.

    What was there before and how was it wired?

    Ceiling Fan Wiring, Ceiling Fan Wiring Technical Help, Do it Yourself (DIY) - Ceiling Fans N More

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Celing fan dual switch [ 1 Answers ]

I am replacing a 20-year old fan with a new Hunter fan. I used dual switch wiring (one switch controls the fan and the other switch controls the light) for the old fan and want to use the same for the new fan. There are three wires in the ceiling (white, black, and groudn). There are four wires...

Wiring for DUAL wall switch to control Ceiling Fan and Light Separately [ 20 Answers ]

Greetings. I recently bought a new ceiling fan and light kit to replace one that had been in my sun porch for over 20 years. A dual wall switch was always used to control the light and fan separately on the older fan. The fan speeds were controlled by pull chain. Before I took the old fan down, I...

Celing Fan Light Switch - 2 Leads [ 1 Answers ]

How do I change the switch on my Hunter fan light? It's not an old unit, but the chain sticks and refuses to release when you pull on it. I bought a replacement switch from Hunter, without instructions. The old switch has two black wires going into the plastic and metal case, with no visible means...

Trouble with ceiling fan on a dual fan/light dimmer switch [ 1 Answers ]

I just installed a new Harbor Breeze ceiling fan and dual fan/light dimmer, also from Harbor Breeze. Unfortunately, now I'm scratching my head... Do I have a bad dimmer switch? Here's the problem: 1. The light will turn on only when the fan speed on the wall switch is set to high. 2. When...


View more questions Search