    Receptacle wiring 230v single phase
    I have a 2hp compressor which is labeled Volts 230/115; PH1. The compressor is not going to be used that often. I would like to plug the compressor into an outlet which was used for a clothes dryer at one time. The outlet has a 10/3 conductor connecting it to double breakers which are labeled 30amps each.
    What kind of receptacle should I use? And how should I wire it?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    May 25, 2010, 03:52 PM

    What is the amps??

    7 amp?
    harrisj214's Avatar
    harrisj214 Posts: 6, Reputation: 1
    New Member
     
    #3

    May 25, 2010, 03:57 PM

    Amps listed on the compressor motor are 11/22
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    May 25, 2010, 04:24 PM
    The 11 is for 230v, the 22 is for 115. If you wire for 230 (240) you should use a dble. Pole 15 amp breaker... with a minimum of 14 ga wire. You can use the 10 ga. but you MUST reduce the breaker size for proper protection of the compressor.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #5

    May 25, 2010, 04:37 PM
    Quote Originally Posted by Missouri Bound View Post
    The 11 is for 230v, the 22 is for 115. If you wire for 230 (240) you should use a dble. pole 15 amp breaker...with a minimum of 14 ga wire. You can use the 10 ga., but you MUST reduce the breaker size for proper protection of the compressor.
    Why must he reduce the breaker size?
    harrisj214's Avatar
    harrisj214 Posts: 6, Reputation: 1
    New Member
     
    #6

    May 25, 2010, 04:45 PM
    So I can use the existing 10 gauge wire, but I would have to change the
    Breaker size from 30 amp to 15 amp. Can you tell me how to connect the wires (red, black, white & ground) to the receptacle? I have a receptacle that is rated 20A, 250V. - it has 2 brass screws and 1 green screw. Can I use that?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #7

    May 25, 2010, 06:29 PM

    You can use both the 30A breaker, and #10AWG. In your case, you would cap the white conductor, and use the black, red, and bare copper conductor. Use a device as required per manufacture.
    harrisj214's Avatar
    harrisj214 Posts: 6, Reputation: 1
    New Member
     
    #8

    May 26, 2010, 05:32 AM

    Can you clarify "Use a device as required per manufacture". Is the device the receptacle? And are you referring to the manufacture of the compressor?
    Also, does the ground wire connect to the green screw on the receptacle?
    And wouldn't I have to lower the breaker size to 15amps to protect the compressor which is rated for 11 amps (as previously mentioned by Missouri Bound)?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #9

    May 26, 2010, 07:28 AM

    Wash,

    I thought that you cannot use a 30 amp CB to protect a 15 amp circuit.

    Is this a situation where you are allowed to do that because this is a motor circuit?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    May 26, 2010, 02:05 PM
    Quote Originally Posted by donf View Post
    Wash,

    I thought that you cannot use a 30 amp CB to protect a 15 amp circuit.

    Is this a situation where you are allowed to do that because this is a motor circuit?

    The breaker protects the circuit conductors, NOT the load. So with #10cu a 30A breaker is fine.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #11

    May 26, 2010, 02:21 PM

    If the 15 amp circuit has a fault, how will a 30 amp breaker react in time to prevent damage, fire or explosion on the devices attached to the 30 amp circuit?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #12

    May 26, 2010, 02:36 PM
    Quote Originally Posted by donf View Post
    If the 15 amp circuit has a fault, how will a 30 amp breaker react in time to prevent damage, fire or explosion on the devices attached to the 30 amp circuit?
    It is NOT a 15A circuit. It is a 30A circuit.

    The motor should have built-in protection. If it does not then it is likely that it would be required, OR it be required to be on a circuit of limited size. This is all based on the motor, not code.

    This is NO different than plugging in a .5A desk fan into a 20A general use circuit.
    harrisj214's Avatar
    harrisj214 Posts: 6, Reputation: 1
    New Member
     
    #13

    May 26, 2010, 02:56 PM
    Quote Originally Posted by stanfortyman View Post
    The breaker protects the circuit conductors, NOT the load. Sow with #10cu a 30A breaker is fine.
    Stanfortyman,

    If I connect a 250v, 20A receptacle to the #10cu should I connect the ground to the green screw, the red & black wires to the brass screws, and then cap the white wire?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #14

    May 26, 2010, 02:58 PM
    Quote Originally Posted by harrisj214 View Post
    Stanfortyman,

    If I connect a 250v, 20A receptacle to the #10cu should I connect the ground to the green screw, the red & black wires to the brass screws, and then cap the white wire?
    Yes, exactly... BUT, if you use a 20A receptacle you MUST then replace the breaker with a 20.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #15

    May 26, 2010, 06:31 PM

    Stan, Thanks for the clarification -
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #16

    May 26, 2010, 07:43 PM
    Harris... let me add to the confusion. Your compressor should have a nameplate somewhere on the motor. Voltage, phase, amperage... etc. There should be a FLA number on that plate which will help you determine what size breaker / overcurrent protection the motor requires. When you use a motor starter, often the protection is on the contactor which starts the motor, in the form of an amperage setting. If you are using a 20 amp receptacle with a 20 amp breaker, you will accomplish the same thing. Is there a pressure switch on the compressor or do you have to add one?
    harrisj214's Avatar
    harrisj214 Posts: 6, Reputation: 1
    New Member
     
    #17

    May 26, 2010, 08:02 PM

    Missouri Bound,
    There is no FLA number on the nameplate. There is a pressure swithch on the compressor.
    Would it make more sense to use a 30 amp receptacle and just leave the 30 amp breaker as is?
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #18

    May 26, 2010, 08:10 PM
    Quote Originally Posted by stanfortyman View Post
    The breaker protects the circuit conductors, NOT the load. Sow with #10cu a 30A breaker is fine.
    Sorry, I've been busy. Seems stan answered the questions you had of me. Thanks stan!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between 3-phase 208 V and single phase 208 V wiring? [ 2 Answers ]

What's the difference between a single phase and a three phase 208V wiring? Does the first has 2 wire only? Can you also identify the wires as to hot, neutral, and ground? This wiring applies to installing an Air conditioning unit. Thanks.

How to wire single phase 208 wiring [ 1 Answers ]

I need to power up a unit requiring 230 VAC single phase. The lab power is 230/3 phase and standard 120 VAC single. What is the correct way to wire this?

Can three single phase loads be driven individually by single three phase supply [ 2 Answers ]

Hi... I am new this community... You are doing great job of knowledge transfer... My question: Can three single phase loads be driven individually by single three phase supply? Please clear my doubt... :confused:

208v single phase wiring [ 1 Answers ]

How do I connect a 208v single phase appliance to my home circuit panel? I installed a 30amp breaker which has 2 connections, red and black (hot), then I have white (neutral), and green for ground. The device only as 2 connectors not 3, plus ground? Thanks

120v/208v single phase appliance wiring [ 2 Answers ]

Recently purchased a coffee machine that has the above reqts. I understand that it has 220 and 110v circuits that need power. I also purchased a generator to power this brewer outside. If I use a NEMA L14-30P plug, to connect into the generator, What is the sequence of wiring for the plug three...


View more questions Search