    Grounding a circuit panel
    I am replacing an old circuit panel with a newer circuit panel with a 100 amp main breaker in it. Do I have to run a ground pole in to the earth and run bare copper wire to the circuit panel?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 23, 2010, 05:44 AM
    Possibly will need to be done. The original system must have been grounded somehow, and it does not necessarily need to be done at the panel containing the Main Breaker, could be grounded at the meter.

    Happen to see a ground wire leaving the meter connecting to a metal water pipe and/or a ground rod?
    davidadrian140's Avatar
    davidadrian140 Posts: 124, Reputation: 2
    Junior Member
     
    #3

    May 23, 2010, 05:13 PM

    Well, there are three wires coming from the meter to the service pane. Two are connected to the 100 amp main breaker and one is connected to the neutral bus bar. There a ground wire that runs from a water pipe to the neutral bus bar inside the service panel. Is this right and should I still do a grounding rod?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    May 24, 2010, 05:33 AM
    If you noticed I did mention a possible ground connecting to a water line.

    This is your primary grounding electrode. Your existing service could be old enough that at the time of install, that was all that was required.

    New code requires when a water line exists, it to be used as a electrode, but that at least one ground rod be installed to supplement the water line.

    Best to check with local codes to determine if more than one rod is required.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

New 250 volt circuit, no grounding bar in main panel [ 4 Answers ]

Hi, I have searched for this answer but I can't find a clear answer for a rookie. I am adding a 250v/20amp circuit to my main panel for a window air conditioner. I have a newer Murray main panel that was installed by an electrician, but its an old house and all the outlets are 2 prong type. So I...

Sub Panel Grounding [ 13 Answers ]

How about if there are only 3 wires in a conduit. Can it be used only as 110v and take one of the hot wires, wrap it with green tape and use it as the equipment ground? An inspector also told me if the panel is in a separate detached building, a ground rod could be used and then you would treat...

Grounding my Service Panel [ 13 Answers ]

I have a 100amp Service Panel which seems adequate for my small 1500 sq' house. I got a quote for a new 200amp panel installed for $2700 so think I'll wait until I expand the house. However, I am converting my plumbing to plastic supply lines and will not have metal to attach the ground to except...

Grounding to Electrical Panel [ 1 Answers ]

I have two 200 Amp meters on a pedistal 10' away from my house foundation. Each will be connected to their own 200 Amp breaker panel with 2" PVC. What is the NEC code for grounding each of these panels. Must each have their own ground rod with #4 bare or can I come from one Ground rod to another 6'...

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...


View more questions Search