    How do I trace a 115 wire from a breaker to an outlet with no electricity
    After a bad storm last night all my garage outlet went out but the breakers are all on. I checked to make sure none were tripped. The lights work in the garage but not the breakers. So how do I trace the 115v line from the outlet to the breaker or vise-versa to find where my problem is?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 21, 2010, 09:48 AM
    You will need an open circuit tracer, something simlar to:

    Greenlee Products - Greenlee A Textron Company

    These cost $500.00 ish.

    You may be able to use a tone generator with a receiver, similar to telephone workers use:

    IDEAL 62-160 Tone Generator, Ideal 62160 - on Sale at the Test Equipment Depot

    But I have not had any luck using these to trace cables, only to find them at one end.
    rtw_travel's Avatar
    rtw_travel Posts: 347, Reputation: 36
    Full Member
     
    #3

    May 21, 2010, 10:06 AM

    Sometimes breakers can appear to be closed, but in fact they are tripped. We have a Square D panel at the cottage that is like that - its really annoying.

    Do you know which specific breaker it is? If you do, then turn it off and back on. That may fix the problem.

    If you don't know which one it is, then you may have to flip all breakers in the panel off then on until you find the right one (but you'll have to reset most electric clocks when you're done).

    If that doesn't work, then can you report back on whether the garage is attached to your house? If not attached, is it an overhead service?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    May 21, 2010, 10:25 AM
    Fred, the simplest thing to do will be to open each outlet, junction box, etc in the circuit from the panel to the device not working and check all connections.

    A popular reason for losing power on part of a circuit is at receptacles, sometimes the connection is nothing more that the wire is stripped and pushed into the back of the device. Call QuikWire, Whiz Wire, etc.

    Change any connections you find like this to wrap around the screw type connection.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #5

    May 21, 2010, 11:11 AM

    Could this circuit be a GFI?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

#2 copper wire rated at 115 feet [ 11 Answers ]

I want to energize a sub panel in my lower garage. I want to have a sub panel rated At somewhere between 70 and 100 amps. What size copper wire can I use to to do this in a romex style conductor ?

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

GFCI breaker w/ 2-wire outlet [ 1 Answers ]

Will a GFCI breaker in the service panel protect a branch circuit without a ground wire? I recently installed a 20a GFCI breaker in my daughter's older home to protect three duplex receptacles - two in the kitchen and one outside the back door. I then discovered that the outlet outside is only a...

How to wire an 15amp dedicated outlet from breaker panel to kitchen [ 1 Answers ]

I need to put a 15 amp outlet that has its own breaker in my kitchen above the cabinets or in cab over oven. This is for a microwave oven. Thanks in advance for any help!


View more questions Search