    Switch triggers GFCI
    My garage had a GFCI outlet in a single gang box. The power to the box also supplied unswitched power to an exterior flood light (with a photoelectric switch in the fixture) and to another box that had the switch for the interior garage light. When the wall was recently removed for an unrelated renovation project, I had the opportunity to replace the single gang with a triple gang box, move the switch and add a switch to the exterior light. I wired the line to the GFCI and the 2 switches to the GFCI's load. (the original switch location became a junction box). All grounds were wired together as were the neutrals. The 2 switches were wired together with a lead from the load of the GFCI. When either switch was turned on, the GFCI tripped. The GFCI worked fine and was checked that it was wired correctly. I solved the problem by wiring the switches directly to the line "behind" the GFCI switch, though I wonder if I am giving up something safety wise by doing so. Was my original wiring incorrect? Am I OK wiring it as is? Thanks.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    May 9, 2010, 07:08 PM
    Although sometimes lights are connected to a GFCI via a receptacle (most commonly in a bathroom) the primary use for a GFCI is protection at the receptacle in wet locations. A GFCI circuit is not required for lighting circuits.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    May 9, 2010, 07:33 PM

    Not sure I follow your post.

    I wired the line to the GFCI and the 2 switches to the GFCI's load.
    That statement gives me concern.

    The line terminals are the connection for the power source. The load side is for any outlets of other devices down stream from the GFI.
    The line side has a silver terminal on the left for the line neutral (white wire). It has a brass terminal on the right for the line hot (black wire). Most GFIs have two sets of load terminals. One set is GFI protected, the other is not. Usually the set in the center is not protected and there is a yellow warning tape that must be removed to use. The unprotected terminals are just another way of connecting load to the line. It is equalivent to wire nuting the two together.
    Light are not required to be GFI protected, only outlets.
    If you chose to use the GFI protected terminals to power the switches to the lights and the GFI trips when you turn the switch on, that means something is wrong with the wiring. If it happens when you turn either switch on, the problem is probably in the way you wired the switches. If the GFI trips when you turn just one of the switch on, the problem is probably in the wiring to that light.

    Post back giving specific wire connections.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    May 10, 2010, 05:16 AM

    If the light switch is fed from the GFI Load side, then the lights neutral needs to be on the load side as well.
    A load needs to be Either on the Line side OR Load side(hot and neutral).
    Your GFI is working fine.
    I wouldn't use the load side, If GFI trips, it would leave you in the dark.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can a GFCI be controlled by a switch? [ 4 Answers ]

I currently have a vanity with a built in light and a built in outlet that is turned on and off by a light switch near the door. I want to remove the vanity, install a GFCI outlet and wire in two new lighting fixtures. I recently read that a GFCI outlet should not be controlled by a switch, but...

GFCI and a light switch [ 1 Answers ]

I am trying to replace a light switch and outlet with a GFCI in my bathroom. The house was built in 1967 so the electrical work is a little shaky. I pulled out the light switch and the old outlet and hooked up the GFCI... and both plugs function properly. The problem is that I can't get the...

3-way switch trips GFCI [ 1 Answers ]

All, I installed a GFCI in a bathroom that has 2 outlets, 2 vanity light bars controlled by a pair of 3-way switches, and a shower room with a Nutone fan/heater/light combo. I installed a GFCI in one outlet and when I turn on the lights, the GFCI trips. Both outlets have two cables in them and...

Is my GFCI switch bad? [ 1 Answers ]

5228 5229I hooked my 2 pole 50 amp GFCI up inline with the house power coming from the circuit Breaker box, the line out to the hot tub isn't hooked up yet. I get readings of 118v from the red to neutral and black to neutral both on the leads from the house power, and also with the switch on,...

GFCI & Switch [ 1 Answers ]

Can a GFCI be wired to run of a switch?


View more questions Search