 |
|
|
 |
New Member
|
|
May 6, 2010, 07:56 PM
|
|
2 separate 120s but no 220
Why don't I get 220 volts when I test the 2 110 legs with a meter?
I get 110 with a meter on each leg separately but when I test the 2 legs of 110 together I don't get any voltage
|
|
 |
Ultra Member
|
|
May 6, 2010, 07:59 PM
|
|
Which 2 legs are you talking about? Are you talking about a breaker, a panel, what?
|
|
 |
New Member
|
|
May 6, 2010, 08:04 PM
|
|
It's the 2 110 legs to my swimming pool motor. I have 2 110 legs and a ground. I know I should get 220 when I touch my test leads to the 2 110s but I'm not
|
|
 |
Ultra Member
|
|
May 6, 2010, 08:07 PM
|
|
So... is this a new installation? Did it ever work? What happened? More detail.
|
|
 |
New Member
|
|
May 6, 2010, 08:09 PM
|
|
Its been working for years,one morning I noticed the pump was off and this is what I'm getting when I test the wiring at the switch and the back of the motor itself
|
|
 |
Ultra Member
|
|
May 6, 2010, 08:12 PM
|
|
It's one of two things... either the breaker has lost a leg, or there is a broken or loose connection. Where does the power come from, the panel or a separate disconnect? You need to check the voltage at the source, if you are capable of doing that.
|
|
 |
New Member
|
|
May 6, 2010, 08:22 PM
|
|
So you think its an electrical problem which is what I thought,but an electrician looked at the problem and said there is nothing wrong with the wiring and said it was the pump motor. But I was sure I should get a 220 reading when checking the 2 110 legs togetherwith a meter. The power comes right from the main panel on the side of the house
|
|
 |
Home Improvement & Construction Expert
|
|
May 6, 2010, 10:24 PM
|
|
Has any other wiring been done which involve opening the circuit panel?
|
|
 |
Ultra Member
|
|
May 7, 2010, 02:06 PM
|
|
Well, if you have 220 (240) at the motor and it doesn't run, it's a motor problem. If you have 110 (120) at the motor, and it's a 220 volt motor... it's an electrical problem. Start by finding a new electrician.
|
|
 |
Uber Member
|
|
May 7, 2010, 05:51 PM
|
|
Just to clear some things up. Having 120, but no 240 can mean:
1. Double pole breaker on same side of line
2. A loose connection/bad breaker.
Picture it this way. Suppose one side of the breaker was open and the motor was on or there was some leakage path in the motor.
The motor winding would act as a wire, essentially showing 120 at both sides.
So, you have to ENSURE the motor is OFF when making these measurements otherwise you can be fooled. The meter draws negligible current.
|
|
 |
Home Repair & Remodeling Expert
|
|
May 7, 2010, 07:04 PM
|
|
If you are actually getting a reading of 110 on your test meter please tell us where you live.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Commual or separate
[ 8 Answers ]
Are my tools I use to make my lively hood community or separate property
Wiring a 220 switch to a 220 Heater
[ 1 Answers ]
I have a 220 warehouse type heater already hooked up in my garage, I going to move it and I want to hook a wall on/off switch to operate it behind my bar (oh you my garage is a full bar :) ) is this possible and can you tell me how the wire configuration would be, box to switch,switch to unit?...
View more questions
Search
|