    How to ground a breaker box
    I have a main breaker box that would be considered a sub panel.(Main shutoff outside on pole) The box is a New Square D Home. The common and ground bars are bounded. It is my understanding the common and ground must be separate in the case.If I am correct, what is the best practice and code for the bare ground wires.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 24, 2010, 03:58 AM
    Only at the main breaker must the neutral be bonded to the equipment ground. The feeder from the main disconnect to the circuit breaker panel must have 4 wires, one insulated for the neutral and one insulated or bare for the equipment ground.

    Downstream of the main breaker, the neutral must be insulated and isolated from all bare or green equipment grounds.

    At the panelboard a separate equipment ground bar is needed for all green and bare grounds, and the bar is bolted to the metal can of the panel using machine thread screws.

    Not sure if this answers your question.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Apr 24, 2010, 09:07 AM
    Why are you thinking it's a sub panel? Every panel has a mean of disconnecting at the pole. Does this panel have a main breaker in it as well?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground wire to neutral bus connection in breaker box? [ 5 Answers ]

In preparation of wiring a hot tub I took off my breaker box panel face plate and noticed that the 8-2 w/g white romex coming into my breaker box had the bare ground wire connected to the neutral bus. The other two hot wires go to the 30 amp breaker. This romex comes from my air cond compressor...

Correct method to RUN copper ground wire to ground a 200 amp electrical circuit box? [ 0 Answers ]

Is a 3-wire copper ground or a solid copper wire required to ground a 200 amp electrical box? Is this wireing correct: A 3-wire copper ground wire in a conduit run from the electrical panel to the copper rod in the ground then to the cold water; AND THEN IN THE GARAGE the naked 3-wire...

How to ground circuit breaker box [ 3 Answers ]

100 AMP Service - Breaker Box - obviously residential. Must you use a grounding rod? If so, how many? Inside or outside the foundation? What gauge (copper wire)?

Why do we need to bond neutral & ground in breaker box [ 5 Answers ]

I have noticed that in the Main breaker box we bond the neutral and ground togather. The questions are; 1- Why do we need to do so. 2- If I plug my drill in to any grounded outlet, why the ground wire is not carring any current as the neutral does and we can touch ground wire where as we can't...

Can Common and Ground Wires be Connected Together in a Breaker Box? [ 9 Answers ]

I am using a spare bedroom for a workshop, and have installed extra lighting, a central vacuum and various power tools. The existing outlets are on two circuits, each with a 15 amp breaker. Both circuits are shared with other rooms and I occasionally overload the circuit and have to reset one or...


View more questions Search