    mohonrim's Avatar
    mohonrim Posts: 7, Reputation: 1
    New Member
     
    #1

    Apr 17, 2010, 10:12 AM
    Heat Pump A/C unit not pumping cold air, but fan is running
    Hello everyone, first time poster so please bare with me.

    We have 2 units, the main floor unit stopped working this week. By "stop working" I mean that the unit will not blow cold air. The fan appears to be blowing because air is coming out of the vents and the air is room temperature. We turned the system off for a couple of days, thinking it may be frozen. However, this did not work.

    We contacted a service company and he came out yesterday afternoon. I was with him as he inspected everything. First he found that the air filter needed to be replaced. His first assumption was that this had caused the system to lock up or something along those lines. Thus, the system was not able to pull air through to cool, causing the system to go into a lockdown mode that shut itself off automatically.

    Then, I left him alone for another 30-45 minutes. He then returned to say that the TXV valve was bad and would need to be replaced. In addition, the freon would need to be flushed and replaced, and the filter that's located near the TXV valve would need to be replaced at the same time. All for $1200-1500 depending on if I bought the maintenance plan or not.

    So, my question is, does this sound right? How can I verify his findings? Can I do this fix myself? We don't have enough money to do this right now, as I've been laid off for over 5 months and only my wife is supporting us.

    Any help or advice is greatly appreciated. Thank you!

    --
    Shane

    This is a Lennox system, 2002, installed in 2003.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 17, 2010, 10:18 AM

    I see no reason the freon would need to be replaced, inless the compressor burnt out. Are you trying to run your heatpump in heat mode or ac?
    mohonrim's Avatar
    mohonrim Posts: 7, Reputation: 1
    New Member
     
    #3

    Apr 17, 2010, 10:19 AM
    Quote Originally Posted by Joshdta View Post
    i see no reason the freon would need to be replaced, inless the compressor burnt out. Are you trying to run your heatpump in heat mode or ac?
    Ac mode. He made no mention of needing to replace the compressor.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Apr 17, 2010, 10:25 AM

    Turn your ac on, let it run for 5 minutes or so. Go outside and see if the fan is running, Feel the air coming from the top of the unit it should be warm. Feel the copper lines going into the unit. The small line should be warm, not hot. And the big cooper line shoud be cold and sweeting. If after 5-10 minutes if
    The outdoor unit will not come on. You can take the pannel off where the electric goes into the unit. There will be a defrost board in there and it should have a flashing red led fault code light.
    mohonrim's Avatar
    mohonrim Posts: 7, Reputation: 1
    New Member
     
    #5

    Apr 17, 2010, 10:40 AM

    Thank you for your response.

    The air is still blowing through the vents, but as before, just at room temperature.

    The outside unit is not running at all, so I took off the cover as instructed. Both LEDs are flashing and based on the board instructions, that means it's "Operating Normally". I checked both of the copper lines, and both the small and the large lines were just normal, i.e. not hot or cold/sweating.

    So, what next? Thank you so much for your help.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #6

    Apr 17, 2010, 10:47 AM

    There is a 5 min time delay on the outdoor unit after your indoor fan comes on. So make sure you have waited for that to cycle out. If you are sure the 5 minutes have passed. You can check for 24 volts, or you can push in the contactor to see if the unit will start manualy. Do you have a volt meter? Is there a set of pins on the defrost board that says test?
    mohonrim's Avatar
    mohonrim Posts: 7, Reputation: 1
    New Member
     
    #7

    Apr 17, 2010, 11:11 AM

    Ok. It's still not running and no change on the lines.

    I do see a test pin. (circled in red in this picture -

    Which wire do I put there? Reading the schematic, it appears that the connector is the black square box sitting at the top of this section, or in other words the third unit from the left. Would I take that black wire and connect it to the test pins?


    I don't have a volt meter, but can get one.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #8

    Apr 17, 2010, 11:16 AM

    From the looks of your picture, the bottom picture, the black contactor on the far right that has the main 240 volt wire going to it. It apears to be pulled in like it is supposed to. There for you have no power to this unit. Check the breaker inside the house and the disconnect outside by the unit if so equipped.
    mohonrim's Avatar
    mohonrim Posts: 7, Reputation: 1
    New Member
     
    #9

    Apr 17, 2010, 11:31 AM

    Ah, okay. Well, no luck with the breakers. Nothing was flipped, but I flipped them anyway and nothing happened. There is a box next to the unit where it appears the power runs through, but it's a no-fuse breaker. Not sure what I can do there.

    Any other ideas?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #10

    Apr 17, 2010, 11:35 AM

    The tech you had out may have put that outside disconnect in upside down to kill power to the outdoor unit, check to see if it pulls out real easy, if so turn it over and plug back in. if still no power you will need to get your hands on a volt meter and check to see if you have 220 volts where the power wire goes to that contactor inside the unit. The breaker inside the house would have probably been a 30 amp double pole
    mohonrim's Avatar
    mohonrim Posts: 7, Reputation: 1
    New Member
     
    #11

    Apr 17, 2010, 02:10 PM

    You were right about the tech switching it upside down. So, it definitely turned on after that was corrected. However, the fan wasn't spinning and the small copper line coming in was HOT. I'm afraid that I'm not going to like your next response. :-)
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #12

    Apr 17, 2010, 02:48 PM

    Sounds like you may have a bad fan motor, or start capacitor. With the power off, can you stick something in and see if the fan will spin by hand? If it does you can turn the power back on and try to spin it to get it started. If it starts then it is probably the capacitor if it does not start it is the motor. The only other thing it could be is if your unit is stuck in defrost mode the fan will not spin either.
    mohonrim's Avatar
    mohonrim Posts: 7, Reputation: 1
    New Member
     
    #13

    Apr 17, 2010, 08:02 PM

    Ok, it started! Thank you! But now I have to buy a capacitor and replace it, correct? I'm sure that will be a lot less expensive. And I can do that myself?Just turn off the power, etc.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #14

    Apr 18, 2010, 05:49 AM

    The capacitor is the big gray 3 pronged thing far left of your bottom picture. Turn off the 220 power at the disconect. Take a srew driver and short out the 3 prongs. A capacitor will hold a small charge if not shorted out. Losen the capacitor and write down what wires are where. You will have a herm block, fan block , and c block c for common.
    Take the capacitor to a heating and ac store they will test it for you to see if it is good or not. Should cost $25 to $40 depending on the size of it. You could get just a small 5 uf fan capacitor, for around $7 but then you would have to do some rewireing

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My central heat and air unit is blowing cold air. The fan cycles on and off but no he [ 3 Answers ]

My central heat and air unit is blowing cold air. The fan cycles on and off but no heat. Really cold today

Air blows cold then stops but unit is still running [ 5 Answers ]

Our ac will be working great and then all of a sudden stop blowing cold air, room temperature air will blow instead which heats the house up quick. If we turn the unit off for an hour or two it normally starts to blow cold air again once it's back on. We've checked to see if the unit if frozen...

Heat pump Out door unit is not running [ 1 Answers ]

I have a carrier heat pump. Coming back from a trip the family turned on the thermostat to emergency heating as the only way to get the house warm. Setting the thermostat to normaly heating, the outdoor condenser does nothing. Main breaker in the breakerbox was tripped. I reset the breaker,...

Air unit is running heat and air at same time [ 2 Answers ]

Air unit is running and heat is staying on at same time

Heat pump , in cooling cyce unit runs no cold air [ 1 Answers ]

1970's heat pump Heil runs in cooling cycle, compressor intermediately runs for approximently 2 seconds, every 30 to 45 seconds, no cold air, all information wirering schematics serial numbers unreadablle or missing, charging ports and service valves was not visiable from service panells, my...


View more questions Search