New Member
|
|
Apr 9, 2010, 02:07 PM
|
|
100 amp sub panel in basement
My Friend is refinishing his basement (1100SF). He currently has a 200Amp Service, but the panel does not have enough Spaces. We want to put in a 100 Amp sub panel in the Basement to include:
50Amp- 5 Ton air conditioning
20 Amp- Dedicated Bathroom Circuit
15 Amp- Lighting Circuit
15 Amp- Receps
15 Amp- Receps
15 Amp- Bedroom
My Main question is what size should I Use for the feeders?
According to NEC table 310.15(B)(6) I could use #4's for the Hots and neutral, but I have also read other places that you cannot use this table And need to use table 310.16
If I can use table 310.15(B)(6) I was planning on running 3 #4 (CU), and 1# 8 (CU)
Voltage Drop will not be an issue, the run will be less than 20'.
|
|
 |
Ultra Member
|
|
Apr 9, 2010, 02:41 PM
|
|
It's a bit confusing, the table references. #2 copper is rated for 100amps, but on service wire #4 copper is rated for 100 amps. I would use the #2, even if it is overkill.
Hopefully some others will chime in this thread with suggestions and comments. And you know to separate the neutral and the ground at the sub panel, correct? And you are correct that voltage drop won't be an issue in that short run.
|
|
 |
New Member
|
|
Apr 9, 2010, 07:39 PM
|
|
So do I need to use 310.16 or 310.15B6? I don't think I need to go overkill as long as it is safe and within code.
|
|
 |
Uber Member
|
|
Apr 10, 2010, 03:50 AM
|
|
Table 310.15-B-6 is only for "main power feed between the main disconnect and the panelboard" that serves all loads associated with the dwelling.
Any branch circuit leaving the man panel, which includes a feeder to another panelboard, must use Table 310.16.
Minimum #3 copper , either THHN/THWN or XHHW insulation, as listed in the 75 Deg C column, is allowed.
Use of the 90 Deg C column is not allowed unless the equipment is rated 90 Deg C, and this is special order, so rarely seen.
|
|
 |
Home Improvement & Construction Expert
|
|
Apr 10, 2010, 04:36 AM
|
|
If all you need is more spaces you could switch out about 7 breakers for twin or slim line (what ever your brand calls them) and eliminate the need for a sub panel?
|
|
 |
New Member
|
|
Apr 10, 2010, 07:25 AM
|
|
TK, Thank you very much for clearing that up.
hkstroud, most of the breakers in there are the tandem breakers. There are only three unused spaces 2 of which will be taken up by the 100 Amp Breaker
Do they make #3/3 wire ?
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Updating service panel to 200 amp with feeder to 100 amp panel in old house
[ 8 Answers ]
I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...
200 amp panel feeding a 100 amp panel roughly 130' away
[ 7 Answers ]
Hi all,
We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away?
I want to use aluminum wire as I think copper would be to costly.
Thanks for your help in advance,
Dude
:eek:
100 amp panel to 200 amp panel
[ 2 Answers ]
I currently have a home with 100 amp service to a 100 amp breaker box. The box is old and should be replaced, can I have a 200 amp box installed even though I only have 100 amp service?
100 amp sub panel from 200 amp main panel
[ 2 Answers ]
We have a 200 amp main panel. We added another floor and decided to add a new sub panel of 100 amps. Is this OK? Should the wire gage be different from 100 maps? Your help is appreciated.
100 amp panel to new 200 amp panel and sub panel
[ 3 Answers ]
I have a very small (1000sq feet) 1920 home in Northern New Jersey which 15 years ago was upgraded to breakers with a 100 amp panel. The whole house does have copper romex in it now, and I am adding a substantial addition (3000 sq feet) to the house and I want to put a sub panel in the new portion....
View more questions
Search
|