    Breaker question
    I have a sub panel (125 Amp Main Lug Load Center) with this Siemens Q21525CT breaker (15/25/25/15 Amp). It's a quad/tandem breaker with two 25Amp breakers common trip. This 25amp common trip is for 2 duplex 220v receptacles (4 outlets) for 4 - 600 watts HID lights which equals 11 amp @ 220v and 2 duplex 5-15 (each one on a 15amp breaker) for 110v (1,000 watts or less for miscellaneous in one 15amp and 800 watts 5000 BTU A/C at the other one). I plan to feed this sub panel with a 30amps double pole breaker. My question is… if I’m only using 11 amps @ 220v that means I have 49 amps for use @ 110v or 19amps only?:confused:
    Attached Images
     
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Mar 31, 2010, 02:39 PM

    Your post is confusing, so I'll try to explain it this way:

    Suppose you have a 30A 240 Breaker
    Power is constant, so you have available 30*240 Watts or
    120*30A + 120 *30A which is 30A per 120 V leg.

    When you have only a 240 V load connected, there is no neutral current.

    If you have a 20A on one 120 V leg and 10 amp on the other 120 V leg and a 5 A 240 V load connected to this breaker you have:

    20+5 on one 120 V leg
    10A + 5 on the other 120 V leg

    And (25-15) or 10A flowing in the neutral.
    editon69's Avatar
    editon69 Posts: 4, Reputation: 1
    New Member
     
    #3

    Mar 31, 2010, 04:21 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Your post is confusing, so I'll try to explain it this way:

    Suppose you have a 30A 240 Breaker
    Power is constant, so you have available 30*240 Watts or
    120*30A + 120 *30A which is 30A per 120 V leg.

    When you have only a 240 V load connected, there is no neutral current.

    If you have a 20A on one 120 V leg and 10 amp on the other 120 V leg and a 5 A 240 V load connected to this breaker you have:

    20+5 on one 120 V leg
    10A + 5 on the other 120 V leg

    and (25-15) or 10A flowing in the neutral.
    I'm using 10/3 to feed this sub panel. Sorry for the confusion Sir. I read at the internet 30amp @ 220v = 60amp @ 110v. My question is if I'm using only 12 amp @ 220v for my lights it that’s means I can use 36 amp (18 x 2) because it’s for 110v or its only 18 amp left for 110v receptacles? Sorry Sir if this doesn't make sense at all
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Mar 31, 2010, 05:30 PM

    OK, I think I get it.

    Fed from a 25 A breaker at 240 V

    12 A at 240 V for HID lighting.

    So you have 25-12 or 13 Amps available at 120 from both poles.

    Thus you have potentially two circuits with 13 A available at 120 V.

    Are we on the same page?
    editon69's Avatar
    editon69 Posts: 4, Reputation: 1
    New Member
     
    #5

    Apr 1, 2010, 04:47 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    OK, I think I get it.

    Fed from a 25 A breaker at 240 V

    12 A at 240 V for HID lighting.

    So you have 25-12 or 13 Amps available at 120 from both poles.

    Thus you have potentially two circuits with 13 A available at 120 V.

    Are we on the same page?

    I want to feed my sub panel with a 30 amps double pole circuit with 10/3 from my main panel. My sub panel has a quad/tandem breaker with two 25Amp breakers common trip for 220v and two 15Amp for 110v. Here is the sequence 15/25/25/15. My lights they are going to use 12 amps from this 30a circuit. That means I can use 18 amps for 110v? Or 36amp because they are only using only 110v? I read at the diy forums that 30amp at 220v = 60amp at 110v
    editon69's Avatar
    editon69 Posts: 4, Reputation: 1
    New Member
     
    #6

    Apr 2, 2010, 07:10 AM
    Quote Originally Posted by editon69 View Post
    I want to feed my sub panel with a 30 amps double pole circuit with 10/3 from my main panel. My sub panel has a quad/tandem breaker with two 25Amp breakers common trip for 220v and two 15Amp for 110v. Here is the sequence 15/25/25/15. My lights they are going to use 12 amps from this 30a circuit. That means I can use 18 amps for 110v? or 36amp because they are only using only 110v?. I read at the diy forums that 30amp at 220v = 60amp at 110v
    I found the answer: I have 5760 watts total, to play with safely, regardless of what voltage. 30a*0.8 = 24a*240 = 5760 watts for constant use

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can we convert the 220v breaker in to 24v breaker(vaccum ckt bkr).how [ 1 Answers ]

Can we convert the 220v vacuum ckt bkr in to 24v vcb? How. Can u explain. Can we use differential relay bkrs in the place of 24v bkr?

Question on proper use of GFIC breaker [ 1 Answers ]

I had some outdoor receptacles recently installed and would like to know if it is proper to put a GFIC breaker in the panel for this circuit and will it protect the receptacles from shorting instead of putting a GFIC receptacle in the circuit?

Breaker question? [ 6 Answers ]

How is everyone one doing? I am new to this site seems like there a lot of good information on hear. So I own my home. I was just curious is per say I have three 15amp breakers, Can I just swap those 15amp breakers with 20 amp breakers or do I have do do some wiring. Hence need an electrician? ...

Breaker Box Question [ 5 Answers ]

I guess it would be better to call it a fuse box... not breaker. I live in a rather old house with k&t wiring. Our box, located in the basement, has all the wiring come in from the top. At the top of the front panel there are two black pull-out things that have markings saying main and off. They...

Question on 12 gauge w/ 15 amp breaker [ 2 Answers ]

Hello, Glad to have found this place. Just had a question regarding 12 gauge wiring. While I know it is unsafe to use 15 gauge for a 20 amp breaker, are there any safety concerns using 12 gauge wire on a 15 amp circuit breaker? Reason I ask is I had recessed lights put in my basement and had...


View more questions Search