    Mar 23, 2010, 06:05 PM
    Can I bunch SER cable, without deration? If so, what is the reference.
    I have already run 1/0 ser cable single phase wire for an apartment feeder to the sub panels. The inspector is telling me I cannot bunch them. I have run them down a hall and had to bunch them approx 18" to get into the panel room. He is saying I have to derate the wires. Is this true? If so it will cost much money.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Mar 23, 2010, 07:04 PM

    When you say bunch do you mean bundle? If so then this only applies if it is over 24".
    The references are NEC: 338.10(B)(4) , 334.80 & 310.15(B)(2)(a)

    If this area is required to be fire stopped then the 24" rule does not apply.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is ser electrical cable [ 5 Answers ]

What is ser cable and the application its use for

SER service cable [ 3 Answers ]

Hello, My service to my house is 200 amps and terminates on the side of my house with a service disconnect located next to the meter... breaker style. This service feeds a sub panel that is where all my circuits terminate. It currently is fed through PVC conduit with Aluminum conductors. I want...

Ser cable [ 1 Answers ]

Can I run it across the driveway,or put in cable box

Securing SER cable at outdoor service switch [ 1 Answers ]

What options for securing 4/0 SER at the outdoor service entrance breaker box - Frame house, service switch located on exterior on siding - thanks

SER Cable [ 1 Answers ]

Is SER cable (0,0,0,2) direct bury, or must it be in conduit?


View more questions Search