    For no reson lost power on two oulets, brakers are OK
    In my Garage I lost power on two outlets, on two separete walls, on outlet 1, I had a drop light and a radio, on outlet 2 an freezer that has been working fine for the past 12 years, the house is 20 years old, other outlets for garage doors and ceiling lights are working fine.
    Took a look at braker box and none are trip, all seemed to be fine.

    Any sugestions, Please.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 22, 2010, 12:29 PM

    Most likely there is a loose connection in one of the outlets, probably at the last working outlet on the circuit.
    maady's Avatar
    maady Posts: 1, Reputation: 1
    New Member
     
    #3

    Mar 22, 2010, 12:38 PM

    You may need to check the fuse box for any blown fuse. If its still okay, you may need to check the continuity from breaker box to outlet. There may be chances when mice cuts the power cable. Ensure that the main breaker is switched off while you open and test the live electrical parts.
    roman067's Avatar
    roman067 Posts: 3, Reputation: 1
    New Member
     
    #4

    Mar 22, 2010, 12:46 PM
    Quote Originally Posted by tkrussell View Post
    Most likely there is a loose connection in one of the outlets, probably at the last working outlet on the circuit.

    Thanks tkrussell

    I will keep that in mind, but I keep thinking this lines don't move at all, the outlet that has the drop light, my son uses it to plug another radio when he exercises, three time a week, does not touch the outlet, he connects the radio to the plug on the drop light, on the other wall I have an up right freezer, that's been working OK for over 10 years.

    I will try to look at the panel next time ( I'm a military retiree with 20+ years in electronics, not electrical, I mean I'm not expert, but not completely unfamiliar either), if nothing else then I will call the local electrician.

    Thanks again.
    roman067's Avatar
    roman067 Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 22, 2010, 12:53 PM
    Quote Originally Posted by maady View Post
    You may need to check the fuse box for any blown fuse. If its still okay, you may need to check the continuity from breaker box to outlet. There may be chances when mice cuts the power cable. Ensure that the main breaker is switched off while you open and test the live electrical parts.
    Thanks maady

    And yeahh the one thing that came to mind was the mouse, which I will not discart, but those cables are pretty hard for a mouse, well who knows.
    I will try to look at the panel next time ( I'm a military retiree with 20+ years in electronics, not electrical, I mean I'm not expert, but not completely unfamiliar either), if nothing else then I will call the local electrician.

    Thanks again.
    mcad's Avatar
    mcad Posts: 12, Reputation: 3
    New Member
     
    #6

    Mar 22, 2010, 04:58 PM

    I would have to second Tk on checking the last working outlet. You would be amazed at what can make a connection come loose. And if whoever installed the outlet decided to use the "mystery holes" in the back of the outlet as opposed to actually wiring to the screw terminal, then it makes it that much more possible.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Mar 22, 2010, 06:20 PM

    Roman,

    The reason you want to check the outlets is because expansion and contraction of the conductors (caused by heat) can loosen connections, particularly if the connections are made using the "Back stabbed" method (the conductors are pushed into the holes on the back of the receptacle instead of using the screw terminals on the side of the receptacle.

    Also, make sure that there is not a GFCI receptacle that has tripped and killed the downstream receptacles.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Reson of black partical in water [ 0 Answers ]

From our ground water we found balck partical in large amount and it is making trouble for R.O.system and chock the PPR pipelines,we have an analysis report as follows Ph-7.4 Turbidity: 5-7 NTU Total hardness: 300 ppm T.D.S.:380 ppm Iron:0.3ppm Above black particals does not remove by birm...

Where is the electric brakers for the hot water tank [ 5 Answers ]

I can't find my electric breakers for my hot water tank

How many oulets on one sercuit [ 1 Answers ]

I am remodeling my basement, To start, I have a 100 amp service box with 14 spaces. Two are the main, 10 are used for the upstairs, and 1 is used for the basement lights. That leaves 1 open for the oulets in the basement. Can I use that 1 to operate 11 outlets in the basement? Or do I have to...

Do you carry circuit brakers for wesco furnaces built in the 1950? [ 1 Answers ]

I need a circuit braker for a wesco furnace heating elements, manufactured in the late 1940 or early 1950, can you tell me where I can find one?

I need to know the reson for the discrepency. [ 1 Answers ]

The researcher states that there were 76 words on the test, but the highest score in the table is 70. Speculate on the reason for this apparent discrepancy. What do you think? :confused:


View more questions Search