    Smoke Dectors
    I have a couple of electrical questions. First has to do with smoke detectors. I will be installing a smoke detector in each bedroom of my house and one in the attic and cellar. Do all of the smoke detectors need to be on the same breaker and wired together (interconnected)? If so I should be using 14-3 or 14-2 (ground wire used to interconnect)?

    The second relates to Arc Fault Circuit Interrupters. I realize all outlets within a bedroom must be wired to an AFCI. What about the Smoke Detectors? I was thinking its better to be safe and simply put them on an AFCI. Will I be able to connect a 14-3 wire to an AFCI?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 19, 2007, 10:34 AM
    Use #14-3 with ground to interconnect all the smokes, do not use a ground wire for this purpose. Use a #14-2 to feed the first smoke then #14-3 to all other smokes.

    A detector is not required in the attic, if this is just a storage space. If the attic can be lived in then yes one is needed. If this attic is just for storage at the most, dust and humidity will cause nuisance tripping. Detectors are only required on level that can be occupied. You may install one in the attic if desired, just be prepared to clean or replace it at some time, and experience false alarms.

    According to the NFPA National Electric Code, a smoke detector wiring in a bedroom area must be AFCI protected. Some states, I know for a fact, have modified this code, and do not allow smoke detectors to be on AFCI protection, due to the conflict of interest.

    If an arc is starting a fire, and an AFCI trips, then the occupant loses the benefit of the detector. You must check with your local and/or state code for their decision on this matter.

    No, a three wire circuit cannot be connected to an AFCI breaker, these breakers cannot protect two circuits with a shared neutral.
    electromechanic's Avatar
    electromechanic Posts: 26, Reputation: 1
    New Member
     
    #3

    Mar 15, 2010, 02:06 PM

    Do smoke detectors need to be in series?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Mar 15, 2010, 04:45 PM
    If you mean one after the other, no. Since the actual wiring is a parallel circuit, they can be wired in any fashion, as long as the 3 wire cable is connected at each location, all blacks together, all whites, and all reds, respectively.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Mar 17, 2010, 05:03 PM

    They actually came up with "Wireless Interconnected Smoke Detectors". You could have 3 smokes interconnected on first floor, 3 wireless interconnected on second floor, If wiring is difficult to get between the 2 sets, use 2 wireless interconnected smokes, 1 on each floor. Expensive, but a time and money saver.
    If interconnecting between detectors is a problem, then you just need to get power and use wireless interconnected smokes and it will solve problem and meet code.
    They are not in series like a Fire System, where removing 1 would violate EOL.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Smoke detectors going off [ 12 Answers ]

Our smoke/fire detectors went off in the middle of the night--the one downstairs first, then the one upstairs, with no detectable cause. We opened some windows and the shrieking stopped. What could have caused this? This morning as we sat at the breakfast table, a bright light flashed above...

Smoke Alarm [ 1 Answers ]

We have a smoke alarm direct wired into the house. It continues to chirp periodically. What causes this and how can we make it stop? Its wired not battery operated so its not a dead battery. Thanks, Eric

Smoke detectors [ 2 Answers ]

Hi, Besides the smoke detector that is require in the hallway, does the NEC require also to install them in all bedrooms or only in the master bedroom? Thanks

Smoke Detectors: Something is not right [ 2 Answers ]

I have 5 detectors in the house: 1 in the basement, 1 in the MBR on the first floor, and 3 upstairs in the bedroom. The detector in the basemet has a Green LED on. I am assuming it is the first detector in that circuit coming from the breaker box. Inside the basement detector are 4 other...

Smoke Alarms [ 2 Answers ]

What would cause all of your smoke alarms to go off at the same time if there is clearly smoke to be detected? They all shut off after approximately 10 minutes.:confused:


View more questions Search