    Dedicated sewage pump vent
    Does a sewage pump vent need to be vented through the roof or can it be spliced into the 4" stack just before exiting the roof? I plan to revent the sink and tub with a separate vent. I have seen this question asked before with different answers.

    Thanks,
    Bob
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Mar 14, 2010, 06:38 AM
    Quote Originally Posted by boblew View Post
    Does a sewage pump vent need to be vented through the roof or can it be spliced into the 4" stack jsut before exiting the roof? I plan to revent the sink and tub with a separate vent. I have seen this question asked before with different answers.

    Thanks,
    Bob
    There's only one answer Bob,
    The pit vent MUST BE A DEDICATED VENT. (see images) You may revent the fixture vent back into the house system but the pit vent can not be revented. The reason for this is while the lavatory and fixture vents just pull outside air into the system to relieve the suction caused by draining waste the pit vent must push air out while the fixtures are discharging into the pit it must also pull air in while the ejector pump's pumping the pit out. It's not good plumbing practice to introduce pressure into a venting system designed to operate under suction.
    Run a separate vent on the pit. Good luck, Tom
    Attached Images
      
    boblew's Avatar
    boblew Posts: 3, Reputation: 1
    New Member
     
    #3

    Mar 14, 2010, 11:59 AM

    Hi Tom,

    Thanks for answering the question. I was afraid you were going to say that. Just out of curiosity, how can some people say that it doesn't need to go through the roof if they are going to pull a permit and have the village inspect it?

    I have had a couple of quotes and both have said that sewage pit can be revented higher up without going through the roof. Also someone told me that it only had to be separate if it was a pneumatic pump.

    It is just confusing that they plan to have the village inspect it if it is going to be against code.

    Your thoughts?

    Thanks!
    Bob
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #4

    Mar 15, 2010, 10:59 AM

    You cannot connect it to the other vent system. Difference between regular vents and sewer ejector vent is that regular vents "suck" air in during flush while sewer ejector vent allows fumes to rise up by gravity to the roof. In other words, it empties sewer ejector pit of fumes. They are both called "vents" but they have different importance in the plumbing system. I hope that will explain why sewer ejector vent has to be dedicated and go all the way to the roof...
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Mar 15, 2010, 04:10 PM

    Codes vary from area to area. This is straight out of my UPC book, 2006 edition, hope it helps: 710.10, upc. Sumps and receiving tanks shall be provided with substantial covers having a bolt-and-gasket-type manhole or equivalent opening to permit access for inspection, repairs, and cleaning. The top shall be provided with a vent pipe that shall extend separately through the roof or, WHEN PERMITTED, may be combined with other vent pipes. Such vent shall be large enough to maintain atmospheric pressure within the sump under all normal operating conditions and, in no case, shall be less in size than that reququired table 7-5 for the number and type of fixtures discharging into the sump, nor less than one and one-half inches in diameter. When the foregoing requirements are met and the vent, after leaving the sump, is combined with vents from fixtures discharging into the sump, the size of the combined vent need not exceed that required for the total number of fixtures discharging into the sump. NO VENT FROM AN AIR-OPERATING SEWAGE EJECTOR SHALL COMBINE WITH OTHER VENTS.
    boblew's Avatar
    boblew Posts: 3, Reputation: 1
    New Member
     
    #6

    Mar 15, 2010, 07:43 PM
    Okay guys. Thanks for all of your help but I am ending up at the same place as when I first asked the question.

    It appears that the correct way is to have a dedicated vent directly through the roof. However, it looks like some places may give a little wiggle room as long as the pump is not air operated.

    I have spent the last week looking at the roofs of houses to see if I can spot two air vents instead of one. Since I have yet to see two on any roof, maybe this is one place that allows a contractor to revent higher up on a non air sewage pump. This also seems to be the only explanation that would allow the contractor to get his job passed by an inspector.

    I guess I should just verify it myself with the village.

    Thanks,
    Bob
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #7

    Mar 15, 2010, 07:50 PM

    Yep, best to check with local authority. However, I do agree with Tom and Milo. Best plumbing practice to terminate roof separately. This way you will sleep better at night, while not worrying about whether it was done correctly or not. Good luck and please do let us know how things work out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Oatey in line vent for sewage pump in the basement [ 14 Answers ]

I am in th process of adding a basement bathroom in my house.I have hired a lic plumber. The plumber is running vent line to the sink the toilet and the shower (Lets call it vent line 1).He than connects this vent line 1 to the vent line coming out of the sewage ejector pump (Vent line 2).He...

Is Meyers pentair sewage ejector pump model SR1830 a quality pump? [ 1 Answers ]

Just installed a sewage ejector pump and I'm somewhat concerned about the manufacture. Not seeing very much information about Meyer. I see Zoeller and Little Giant, so I'm wondering if I got a quality systems. Considering all that was required to get the system in I don't want to revisit this for...

Basement sewage pump vent [ 5 Answers ]

I would like to add a drian line from my bar sink to the sewage basin in my basement. Can I tap into the vent line of the basin to drain this sink? It's a 2" vent and the drain line is 2". Dbrown39


View more questions Search