    Is a ground rod needed for a subpanel?
    I have installed a 60 amp subpanel in my house flush mounted on a wall separating 2 rooms. I ran 6/3 romex for the 2 hots, 1 neutral and ground from the main panel that is outside.
    My question is do I need a separate groundind rod?
    If so what is the furthest I can put the rod?
    Also can the bare gec be ran through the attic crawlspace to the subpanel.

    The nearest exterior wall is about 8ft would this OK. I have the nec 4th edition book and I can not an answer. I have read some of the other post and there contradicting each other.

    Need some guidance.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 12, 2010, 03:32 AM
    A subpanel in a building that already contains the main service, which is grounded, does not need another grounding electrode.

    Just be sure to use the insulated neutral bar in the new panel for all white neutrals, do not install the green bonding screw, and use a separate equipment grounding bar, bolted to the panel box using machine screws for all green or bare grounds.
    SAISKY's Avatar
    SAISKY Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 12, 2010, 11:43 AM
    Thank you very much for the answer tkrussell, now I can call for the rough inspection. Ive been holding off cause I couldn't get a straight answer.

    Yeah I used the neutral bar that came with the panel it's sitting on rubber stoppers or it looks like that is what I mean. I do have the ground on a separate bar as well.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground rod wire is not connected to the ground rod [ 1 Answers ]

My inspection report for a property that I'm looking to purchase said that my " ground rod wire is not connected to the ground rod". I have no idea what something this would cost to fix. He also said that the ground rod clamp was rotten. Am I looking at thousands in repairs?

Ground rod location [ 1 Answers ]

I am running service to detached garage apt. Here's the basics: underground service from utility's pole to meter can at rear of house. Then directly adjacent and connected by 2" pvc , second , un-used meter can. From there 2" PVC under ground to new 200AMP distribution panel in interior of garage....

Ground rod instead of ground wire? [ 7 Answers ]

I'd like to install an RV outlet (120v, 30amp) in our parking area. Unfortunately, I only have two wires available to that location and adding a third wire would be quite difficult. Can I use the two available wires for hot and neutral and drive in a grounding rod next to the outlet for the...

Ground Rod / ground wire [ 9 Answers ]

Hello, I am installing a 100 amp subpanel in my workshop 125' away from my house. I have two ground rods in the ground by the shop, and was wondering if it was necessary to run 4 wires from the house to the shop (two hots, one neutral, one ground), or could I just run the three wires from the...

Dose a newly added subpanel need a grounding rod? [ 5 Answers ]

I'm goining to add a new subpanel to a detached garage , for a 6-3g 240v outlet for use with mechanic's tools (small mechanic work) and a few 120v outlets and mabe a over head light (florecent) Now I've studied the panel info I've found online but haven't came across the QUESTION of Do I need to...


View more questions Search