    Blower fan on with no heat and no error code
    Hello,

    My low efficiency Heil furnace will intermittently fail to turn on the main burners. The exhaust vent fan starts, the glow plug lights, piolet light ignights, the main blower motor turns on and remains on, but the main gas burner never fires. It seems like the gas never turns on and the blower will run until power is turned off. Sometimes we have to cycle the power a few times to get the main burner to fire and then all is well for a few days.

    Two days ago I replaced the old main timer board with one that has a status light (Honeywell ST9120U). While behaving as previously described, the st9120U status light is a dim-blink-dim-blink pattern that is defined as a heartbeat (no error code). Any ideas?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 1, 2010, 01:16 PM
    Exact model number of Heil furnace?
    Princeton_MN's Avatar
    Princeton_MN Posts: 4, Reputation: 1
    New Member
     
    #3

    Feb 1, 2010, 01:22 PM

    Model number NTC6075FBA1
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 1, 2010, 01:56 PM
    Here is your manual

    http://icpindexing.mqgroup.com/docum...4101230604.pdf

    Look over the pilot flame picture and see if it looks like the flame on your pilot. If the pilot flame is incorrect it will not hit the flame sensor portion of the pilot and the furnace will not activate the gas and lock out with blower staying on.
    Princeton_MN's Avatar
    Princeton_MN Posts: 4, Reputation: 1
    New Member
     
    #5

    Feb 1, 2010, 03:18 PM
    Thanks for the manual link.

    The pilot flame is good. The temp sensor glows red hot. I cut the wire to the temp sensor. If I make a break in the wire the pilot goes out. I also pulled 1 wire at a time on each of the temperature sensors and watched the pilot lite go out each time. I did this again for the exhause blower switch with the same result. Any other ideas?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Feb 1, 2010, 05:19 PM
    Make sure the ground from the electric breaker panel to the unit is good and making a good connection. That is the bare copper or green wire. That control you are using likes a very good ground. NOW I am not talking about the white neutral wire but the ground.

    Hook your meter up to the gas valve and make sure it is getting the proper voltage when the unit should be running. If no voltage to the gas valve it will not open for gas flow. Also if voltage is going to gas valve and it will not open it is a bad valve.
    Princeton_MN's Avatar
    Princeton_MN Posts: 4, Reputation: 1
    New Member
     
    #7

    Feb 17, 2010, 08:53 AM
    There have been no problems in over a week since the electronic gas valve was replaced. In hindsight, I should have verified there was voltage at the valve wiring harness when the gas burner was not working prior to replacing the control board. However, the control board was less then $100, easy to replace, and over 10 years old. Electronics tend to fail between 10 and 15 years anyway.

    Thanks for the help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Feb 17, 2010, 09:05 AM
    At least you now have some heat and that is all that counts.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower on after power up error code 12 Carrier 58RAV [ 2 Answers ]

I have a "blower on after startup (115v or 24v)" error 12 going on. When I shut down the power for 15 minutes and restart. The unit right away starts the blower and thats it! No attempt to ignite at all. The blower just blows colds air and does not stop. Any suggestions on this would be great. I...

Trane XE80 furnace occasionally produces no heat, error code 4 [ 3 Answers ]

Hello, I have a Trane XE80, model number TDD080C936E0. A few weeks ago, it started blowing only cold air with error code 4 - high temperature limit open. If I shut it down, and start it up again in about an hour or so, sometimes it comes back on, sometimes it doesn't (produce cold air only). ...

Fan Blower doesn't come on in Fan,heat or cool [ 2 Answers ]

Yesterday I turned on my heat(coil in air handler) and everything worked fine. Last night I turned it on again and the fan wouldn't come on no matter where the switch was: fan only, heat or air. I made the appropriate temp changes for heat/air. There is a humming noise coming from the heating coil...

Blower fan works in A/C but not heat [ 8 Answers ]

A couple of weeks ago my Lennox G20Q3E-75-1 was acting up. Gas valve was cycling when calling for heat and then once satisfied and the main burners went out the pilot light was staying lit. I thought it might be the flame sensor as far as the gas valve cycling and didn't want to tear into it so I...


View more questions Search