    I have 10-2 wire and a 30amp breaker. The wire has 4 wires in it,blk-red-wht-and grn.

    The welder has 3 wires extending from it, blk-wht-and grn

    How should this be done?
    trentonmakes's Avatar
    trentonmakes Posts: 3, Reputation: 1
    New Member
     
    #2

    Jan 31, 2010, 04:58 PM

    I'm guessing I could put the blk and what wire to the hot on the plug and grnd to grnd and bypass the neutral since there's no wire for it to connect the plug.

    Then use the red and blk wires from breaker to the outlet along with the neutral and ground wires
    Then
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jan 31, 2010, 05:29 PM

    Put the red and black wires on the 240 breaker. White can be connected to neutral at the box and ground to ground.

    At the welder plug, use black and red and green, where green is ground. Put a wirenut on the white.

    On the plug of the welder, use black and white and attach to the red and black wires from the breaker respectively Green goes to green.
    trentonmakes's Avatar
    trentonmakes Posts: 3, Reputation: 1
    New Member
     
    #4

    Jan 31, 2010, 06:28 PM
    The welder wiring to the plug is only blk,what,and green. Im planning on using the white as hot/red as it would be the only way to get the 240 from the outlet.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Jan 31, 2010, 06:32 PM
    Are you sure it's a 240volt welder?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Jan 31, 2010, 07:05 PM

    What you have is a 10/3 cable. You can actually use a 10/2 cable.

    If this is a straight 240 VAC unit and not a 120/240 VAC unit, then either red or white is not needed.

    You would connect the Black conductor to the black on the unit and then use either the red or white wire connected to the white on the white.

    The other end of the conductor would go to the second phase position on the breaker. If you choose the white conductor, then use either black electrical tape or a black sharpie to color the insulation at both ends so you know that it is a hot conductor. Also, make sure you cap off both ends of the ed conductor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Implications of using a 240 line for a 208 kiln [ 7 Answers ]

I have a 56 amp, 208 volt ceramic kiln that I need to hook up to residential service. It's basically an overgrown toaster oven. Is this even possible and if so what effect will it have on the equipment?

Do I need a dedicated line for a 9 amp AC running on a 20 amp breaker? [ 1 Answers ]

Do I need a dedicated outlet for a 10,000 BTU 9 amp AC running on a 20 amp breaker? This is in a Bedroom with Clock radio, light fixture and a TV.

240 Line Volt Thermometer [ 2 Answers ]

Where can I get a good 240 line volt thermometer? The one installed in my attic (bedroom) is a beastly clunky p.o.s. with a big dial that's hard to turn. Can I get a nice digital one? I haven't found a good one yet. Thanks!

240 line to 110 [ 4 Answers ]

My question is, how do I take a line that is wired to both terminals of a double 20 amp breaker and make it so I can use it as a normal 110 volts service for a switch. To start I found that a meter reading of 110 volts was achieved by putting the terminals on either the black or white wire and the...

Lengthening 240 line [ 4 Answers ]

The 240 line that was installed for my oven is just about 3 inches to short to allow the plug to rest in the recessed area of the range. Therefore, the range sits about 1 1/2 inches from the wall and it's driving me crazy. Can additional wire be spliced to the end of the existing in order to...


View more questions Search