    Low line-to-neutral voltage
    Hi,

    Recently, the power of my house was out. After the power was resumed, three of the outlets in my bathrooms were not able to be used. I've measured the voltage between line and neutral with a DMM and received a very low voltage reading of approximately 0.5V. Between GND and line is 120V (as expected). No device was plugged into any of those outlets. I don't know what to do at this point; could anybody please help me to figure out the problem? I really appreciate any help. Thanks.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jan 31, 2010, 12:28 PM

    Bathrooms require GFCI protection. Look at the receptacle, does it have a test or reset button?

    If not check the other two receptacles. When you find the correct receptacle, reset it.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 31, 2010, 01:41 PM
    The circuit has an open neutral conductor. Each box between the panel and the outlet being affected will need to be check for a loose or broken connection on the white wire.
    doithay's Avatar
    doithay Posts: 2, Reputation: 1
    New Member
     
    #4

    Feb 1, 2010, 08:13 AM

    Thanks all for your helps.
    I've figured out the problem. I've found and reset the GFCI in another bathroom downstair and everything is back to normal. I thought that every single bathroom should has its own GFCI? In this case, only one GFCI is used for all three bathrooms in my house; is this normal?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Feb 1, 2010, 08:19 AM
    Sure, it is done often, one GFI device can protect as many standard receptacles as necessary, within the amp ratings of the GFI device.

    Because of the symptom you reported:

    "I've measured the voltage between line and neutral with a DMM and received a very low voltage reading of approximately 0.5V. Between GND and line is 120V "

    I suspect there is still an existing wiring problem. You should not have seen any voltage across the line and neutral AND the line and ground, once a GFI has tripped.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Halogen - line voltage (120v) or low voltage (12v) [ 5 Answers ]

Hi. I am renovating the kitchen and plan to install small halogen MR16 ceiling pot lights. Contrast and Lightolier have been recommended. At least, the Contrast line is available with either line or low voltage feeds. These questions come up as the plan calls for 9x35w MR16 (ceiling pot...

Track lights: low voltage vs line voltage.comsume the same electricity in the end? [ 11 Answers ]

Hi! I just installed a section of track light in my living room just to see what it would look like and so far I'm not convinced... you see, I had a regular celing lamp with a 75w incandescent bulb and the room was very well lit... now with the track light I find that I need 3 fixtures with halogen...

Low voltage or line voltage? [ 3 Answers ]

I have electric ceiling heat. How can I tell whether my thermostats are low voltage (24 volt) or line voltage (120 or 240 volt)?

Low voltage between Ground and Neutral [ 1 Answers ]

I am new to this forum and this is my first question. Should a properly wired 110 Volt house circuit have measurable or any voltage at all between the Neutral and Ground wires? Please advise if more specifics are required for a complete answer. Thank you, Bernard

Voltage on neutral [ 3 Answers ]

I just ran a completely new 10 gauge wire for my newly relocated clothes dryer. I wired up the breaker and turned if off, and turned the main breaker back on. When I measure voltage between the black and white OR between the red and white even though the breaker is OFF I get 1.3 volts. How...


View more questions Search