    sbinns2 Posts: 12, Reputation: 1
    New Member
     
    #1

    Jan 28, 2010, 06:30 AM
    My heat pump will not come on.
    My heat pump will not come on. Checked the breakers they are working. The compressor does not come on when thermostat is turned up. System worked last week.
    Is there a way to by pass the thermostat to check the problem?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 28, 2010, 07:27 AM
    Did you check the fuses or circuit breaker in the outside disconnect located near the outside unit?
    sbinns2's Avatar
    sbinns2 Posts: 12, Reputation: 1
    New Member
     
    #3

    Jan 28, 2010, 07:43 AM

    Checked outside disconnect on compressor it seems inserted proper. Checked disconnect on air handler that has the heat strips and hot side seems plastic melted and metal connect fused together.
    Seems it should have tripped the breaker, should I turn off breaker and replace entire disconnect?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 28, 2010, 11:30 AM
    Post pictures if you can but I cannot see the problem from here. Usually when I have had this problem I replace the entire disconnect/or assembly if it has been overheated especially if the buss bars are blue or off color from overheating.
    sbinns2's Avatar
    sbinns2 Posts: 12, Reputation: 1
    New Member
     
    #5

    Jan 28, 2010, 02:01 PM

    Am going to replace the entire disconnect box. Do not understand why main breakers in panel box did not trip. Hope the heat strips were not damaged.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jan 28, 2010, 06:14 PM
    Strips should be OK but a visual inspection for sag and broken elements is in order.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

Carrier difference between 13 seers heat pump and 15 seers heat pump [ 3 Answers ]

I'm changing my heat pump system. I got a quote for a Carrier 13 seers unit. My house is 2200 sq. ft. ranch house with 9' ceilings. Do I need to upgrade to a 15 seers unit. I have no shade on the house. I just want to make the right choice.

Is a heat pump with emergency heat a multi stage heat pump [ 1 Answers ]

I am trying to replace the thermostat for my heat pump the one I've got seems to be running the emergency heat only. All wires were connected as they were in the old one. Is regular heat and emergency heat considered multi-stage? If so, I need another thermostat... please advise.

My Trane Auxiliary heat on heat pump is tripping breakers. I think all 3 elements are g [ 0 Answers ]

All 3 white control wires on 3 contactors to elements gets energized at the same time even when only calling for 2-3 degrees increase. Is that normal? I thought it was setup to increase elements based upon the amount of heat called for? The point is breakers keep tripping in winter for the last...

Propane heat pump vs electric heat pump [ 1 Answers ]

I am trying to calculate the cost of a propane heat pump vs electric heat pump. I currently have an electirc heat pump but am looking to install a new one and don't know whether it is less expensive to have the propane one installed or the electric. We don't have any natural gas lines in our area...


View more questions Search